Thank you all! These discussions are exactly what make this forum such a
valuable informational asset! 

 

All of the replies gave valuable insight into how this arrangement could be
interpreted, as well as misinterpreted to believe there was a greater hazard
present than there is. It is also reassuring to have you all look at the
issue with "new eyes".

 

Thanks again

 

John Paulsen

Crown FSD 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, December 8, 2016 2:42 PM
To: [email protected]
Subject: RE: HDPE Plastic Bin Box Storage

 

What has been described are often referred to as folding bulk containers,
folding pallet containers or similar.   They are open on the top and are
designed to be stacked on upon another directly on the floor.  No racking is
required.

 

Each empty container can represent approximately 80-150 lbs or more of a
Group A plastic.

 

The cited conditions are only stacked two units high.

 

NFPA 13 Chapters 16 and 17 are related to rack storage, the description of
the condition does not include racks.  So those portions of the text are not
applicable to the topic.

 

Since the commodity within pose no fuel load, the exposed plastic container
is the item of concern as far as its exposure to sprinkler discharge.  If
and that's a big IF, a container were to collapse, spillage of the contents
has no impact on fire growth and the collapse of the unit would expose more
surface area of the unit to the sprinkler discharge.

 

Essentially you have a palletized plastics commodity.

 

Back to 15.2.6(a) Col. E based on decision tree 15.5.2 for Group A,
Nonexpanded, Stable, Exposed.

 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 



 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jim Davidson
Sent: Thursday, December 08, 2016 2:27 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage [EXTERNAL]

 

John,

 

Open top HDPE Plastic Bin boxes is a configuration of storage not covered by
NFPA 13 since the open top bin boxes stops the sprinkler water discharge
form delivering the required delivered density. Additionally NFPA 13 2016
edition; 

1.       Paragraph 16.1.7 states 16.1.7 Open-Top Containers. The protection
of open-top containers shall be  considered outside the scope of Chapter 16.
See Section C.12. And 

2.       Paragraph 16.2.3.3 ESFR sprinklers shall not be permitted to
protect

        storage with open top containers.

3.    Paragraph 16.3.3.2 ESFR protection as defined shall not apply to the
following:

(1) Rack storage involving solid shelves, except for situations complying
with 16.3.3.2.1

(2) Rack storage involving open-top cartons or containers. 

4.    17.1.6 Open-Top Containers. The protection of open-top containers is
outside the scope of Chapter 17. (See SectionC.12.)

5.    Paragraph 17.2.3.1.1 ESFR protection as defined shall not apply to the
following:

(1) Rack storage involving solid shelves, except as permitted by 17.2.3.1.2

(2) Rack storage involving open-top cartons or containers

6.    Paragraph 17.3.3.1.2 ESFR sprinklers shall not be permitted to protect
storage with open-top containers.

 

The following is Appendix "A" explanation  A.3.9.1.19 Open-Top Container.
Open-top containers can prevent water from running across the top to storage
and

down the flues and can also collect water. The container will prevent water
penetration to a fire in lower levels where it is needed. Rack or flue
collapse can also occur if too much water is collected. Consideration should
be given to the potential degree of water collection possible within the
container when applying the definition of an open-top container. The
following  conditions should be considered:

(1) Small openings at the top of containers containing such items as fresh
produce are quite common and should not be considered as an open-top
container.

(2) Arrangements that include open-top containers that are all located on
the bottom tier of rack storage do not prevent penetration of water and
should not be considered an open-top container.

(3) Containers having either wire mesh siding or large uniform openings
along the bottom perimeter of each container, such that water enters the
container at the same flow rate and discharge evenly into the flue spaces
should not be considered as an open-top container provided the contents of
the container are not water absorbent and are not capable of blocking such
container openings.

 

The protection of this type of storage is clearly not under the "practice"
of a NICET tech following the prescribed protection guidelines of a
published NFPA standard (White Paper developed by SFPE, NICET and NSPE)
especially since the standard states many times that open-top containers are
not covered by the standard. The specifying engineer might be "outside"
his/her "area of competence" as defined by the Professional Engineering Laws
and Code of Ethics formulated by the state or commonwealth they are
"practicing" in. 

 

Just my two cents and interpretation by a NICET Tech when NFPA 13
specifically states that the protection of open top containers are outside
the scope of specific NFPA 13 chapters could be considered the practice of
engineering and subject their company to an E & O exposure not covered by
the company's insurance policy. 

 

Why expose yourself and your company to such an exposure.

 

Have a fire safe day!

 

Regards

 

Jim

 

 

 

Davidson Associates



Fire Protection Engineering
P. O. Box 4002

Code Consultants
Greenville, DE  19807

 
(302) 994-9500

 
Fax (302) 994-3414

 

CONFIDENTIALITY

This report and any attachments are confidential and also may be privileged.

If you are not the named recipient, or have otherwise received this report
in error, please destroy the report, notify the sender immediately, and do
not disclose its contents to any other person, use them for any purpose, or
store or copy them in any medium.

Thank you for your cooperation.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 11:31 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage

 

Jeff:

 

I appreciate your "caution" on this and perhaps I am overreaching here. But
in my view, I'm just trying to correctly interpret the commodity
classification and arrangement as it relates to the storage provisions of
NFPA-13, which should fall under my practice. In fact, I am working with a
specifying engineer on this who is just as baffled by the insurance
underwriter's concerns as I am. The problem is, this arrangement is not
"specifically" addressed in 13. Is this bin box storage, (it's not cardboard
or corrugated) or open container storage? From everything that I can tell,
if it meet the OHII curve, that should be the governing requirement. 

 

Thanks,

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jeff Hewitt
Sent: Thursday, December 8, 2016 11:03 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage

 

John,

 

I'm writing off on the forum because I don't want to stir up a hornets nest.

 

Isn't this an engineering decision, not a NICET SET decision?

 

I'm just saying, why would you want to take that liability as a NICET SET,
and also potentially violate your NICET Certification by practicing
engineering.

 

Jeff Hewitt, PE, SET, PM.SFPE

Corporate Engineer

 

      

American Fire Protection, Inc.

5525 Eastcliff Industrial Loop | Birmingham, AL  35210

205-591-9111 ext. 1452 | 205-317-0918 (cell)

205-591-9990 (Fax)

 

          

 

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX

Fire sprinklers save lives.  Can you live without them?

 

Please note that any positions expressed above are my professional opinion
only, as a member of the NFPA 13 Technical Committee, and do not represent
an official interpretation of the NFPA 13 standard.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 9:43 AM
To: [email protected]
<mailto:[email protected]> 
Subject: HDPE Plastic Bin Box Storage

 

Hello All!

 

I am working with a truck parts supplier who has moved into an existing
warehouse and I am providing a design study to them on the existing system.

 

Pertinent Facts:

 

6"x6"x2" Grid with K-8.0 Upright Heads fed by a pump. Pipe is at 25' AFF.

Metal truck parts storage in HDPE Plastic Bin Boxes stored no higher than
10'

Existing system with 500 GPM hose calcs to .60 GPM / 3,000.

Tokyo Mutual Insurance

 

Personally I think the system provides adequate protection for the storage
configuration. In fact it is MORE than sufficient according to NFPA 13, Ch
14.  However the insurance company is maintaining that the plastic bin
storage boxes represent an additional hazard. This is a new experience for
me. My contention is that the Bin Boxes, even though they are made of HDPE
Plastic, do not represent an increase to the commodity classification
because of their higher flash point. (which is information I can't seem to
find right now)  

 

Is there a fire test out there that indicates these bin boxes represent an
increased hazard?

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to