Right. 

 

Metal truck parts in these plastic bin containers. Miscellaneous Storage
still applies.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Larry Keeping
Sent: Thursday, December 8, 2016 2:07 PM
To: [email protected]
Subject: RE: HDPE Plastic Bin Box Storage

 

When I read your 1st e-mail/question, I thought the subject was relative to
a truck parts supplier/warehousing operation. 

If that is correct and the facility is dedicated to storage, and the Group A
plastics are being stored at a height greater than 5 feet, I don't think you
should be using the Miscellaneous Storage design criteria from Chapter 13.
Shouldn't you be looking at Chapter 15?

 

Larry Keeping

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Paulsen
Sent: December-08-16 1:52 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage

 

Thanks Craig:

 

These bins are 48" square "folding pallet containers" stacked by two's.
There is no shelving or racking involved, so as a percentage, there is far
less plastic than metal.

 

My thinking is to apply 13.2.1 Group A Plastics - "unexpanded/Expanded" -
>5' <10' = EH2 (.4 over 2,500) 

 

The existing overhead system will provide .6/2,500 with a 40% safety margin.


 

Thoughts - Arguments?

 

Thanks,

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected] <mailto:[email protected]> 
Sent: Thursday, December 8, 2016 12:05 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage

 

Their concern is whether or not the plastic bins are being considered, not
just the stored Class I (metal parts) commodity and it's a valid point if
there are a considerable amount of bins.  If it's one or two short shelves
maybe it's not a big issue with a .6 density, but that would be an AHJ and
Insurer call.

 

HDPE falls into the Group A plastics category.  

 

The metal parts are irrelevant to the case.  You have shelves full of
plastic bins. If the bins were empty how would you classify the storage?

 

If you look at NFPA 13 (2013) Table 15.2.6(a), for storage >5ft but ?12ft,
Roof/Ceiling height at >20 to 32ft (you said system pipe was at 25 ft), the
density shown is 0.7 gpm/sf for Nonexpanded, stable, exposed. 

 

If in fact your final analysis of the design criteria does show a
requirement of .7 gpm/sf, I'd calculate the existing systems as-is and see
if it can meet that criteria.  You might not need to change anything other
than prove it works as-is.  Then you'd also need to be sure the water supply
is adequate for the increased flow demand.  The other thing to consider is
the NFPA 13 criteria only requires calculating of a 2,500 sq. ft. hyd. area,
the 3,000 sf area sounds like an insurer requirement so you may have some
wiggle room there hydraulically if you compare the 0.6@3000
<mailto:0.6@3000>  to 0.7@2500 <mailto:0.7@2500>  but you won't know for
sure until you run the calc.

 

I would be looking at the plastics, not the metal parts.

 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 11:29 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage [EXTERNAL]

 

Jeff:

 

I appreciate your "caution" on this and perhaps I am overreaching here. But
in my view, I'm just trying to correctly interpret the commodity
classification and arrangement as it relates to the storage provisions of
NFPA-13, which should fall under my practice. In fact, I am working with a
specifying engineer on this who is just as baffled by the insurance
underwriter's concerns as I am. The problem is, this arrangement is not
"specifically" addressed in 13. Is this bin box storage, (it's not cardboard
or corrugated) or open container storage? From everything that I can tell,
if it meet the OHII curve, that should be the governing requirement. 

 

Thanks,

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jeff Hewitt
Sent: Thursday, December 8, 2016 11:03 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: HDPE Plastic Bin Box Storage

 

John,

 

I'm writing off on the forum because I don't want to stir up a hornets nest.

 

Isn't this an engineering decision, not a NICET SET decision?

 

I'm just saying, why would you want to take that liability as a NICET SET,
and also potentially violate your NICET Certification by practicing
engineering.

 

Jeff Hewitt, PE, SET, PM.SFPE

Corporate Engineer

 

      

American Fire Protection, Inc.

5525 Eastcliff Industrial Loop | Birmingham, AL  35210

205-591-9111 ext. 1452 | 205-317-0918 (cell)

205-591-9990 (Fax)

 

          

 

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX

Fire sprinklers save lives.  Can you live without them?

 

Please note that any positions expressed above are my professional opinion
only, as a member of the NFPA 13 Technical Committee, and do not represent
an official interpretation of the NFPA 13 standard.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 9:43 AM
To: [email protected]
<mailto:[email protected]> 
Subject: HDPE Plastic Bin Box Storage

 

Hello All!

 

I am working with a truck parts supplier who has moved into an existing
warehouse and I am providing a design study to them on the existing system.

 

Pertinent Facts:

 

6"x6"x2" Grid with K-8.0 Upright Heads fed by a pump. Pipe is at 25' AFF.

Metal truck parts storage in HDPE Plastic Bin Boxes stored no higher than
10'

Existing system with 500 GPM hose calcs to .60 GPM / 3,000.

Tokyo Mutual Insurance

 

Personally I think the system provides adequate protection for the storage
configuration. In fact it is MORE than sufficient according to NFPA 13, Ch
14.  However the insurance company is maintaining that the plastic bin
storage boxes represent an additional hazard. This is a new experience for
me. My contention is that the Bin Boxes, even though they are made of HDPE
Plastic, do not represent an increase to the commodity classification
because of their higher flash point. (which is information I can't seem to
find right now)  

 

Is there a fire test out there that indicates these bin boxes represent an
increased hazard?

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to