What has been described are often referred to as folding bulk containers, 
folding pallet containers or similar.   They are open on the top and are 
designed to be stacked on upon another directly on the floor.  No racking is 
required.

Each empty container can represent approximately 80-150 lbs or more of a Group 
A plastic.

The cited conditions are only stacked two units high.

NFPA 13 Chapters 16 and 17 are related to rack storage, the description of the 
condition does not include racks.  So those portions of the text are not 
applicable to the topic.

Since the commodity within pose no fuel load, the exposed plastic container is 
the item of concern as far as its exposure to sprinkler discharge.  If and 
that's a big IF, a container were to collapse, spillage of the contents has no 
impact on fire growth and the collapse of the unit would expose more surface 
area of the unit to the sprinkler discharge.

Essentially you have a palletized plastics commodity.

Back to 15.2.6(a) Col. E based on decision tree 15.5.2 for Group A, 
Nonexpanded, Stable, Exposed.



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jim Davidson
Sent: Thursday, December 08, 2016 2:27 PM
To: [email protected]
Subject: RE: HDPE Plastic Bin Box Storage [EXTERNAL]

John,

Open top HDPE Plastic Bin boxes is a configuration of storage not covered by 
NFPA 13 since the open top bin boxes stops the sprinkler water discharge form 
delivering the required delivered density. Additionally NFPA 13 2016 edition;

1.       Paragraph 16.1.7 states 16.1.7 Open-Top Containers. The protection of 
open-top containers shall be  considered outside the scope of Chapter 16. See 
Section C.12. And

2.       Paragraph 16.2.3.3 ESFR sprinklers shall not be permitted to protect
        storage with open top containers.
3.    Paragraph 16.3.3.2 ESFR protection as defined shall not apply to the 
following:
(1) Rack storage involving solid shelves, except for situations complying with 
16.3.3.2.1
(2) Rack storage involving open-top cartons or containers.
4.    17.1.6 Open-Top Containers. The protection of open-top containers is 
outside the scope of Chapter 17. (See SectionC.12.)
5.    Paragraph 17.2.3.1.1 ESFR protection as defined shall not apply to the 
following:
(1) Rack storage involving solid shelves, except as permitted by 17.2.3.1.2
(2) Rack storage involving open-top cartons or containers
6.    Paragraph 17.3.3.1.2 ESFR sprinklers shall not be permitted to protect 
storage with open-top containers.

The following is Appendix "A" explanation  A.3.9.1.19 Open-Top Container. 
Open-top containers can prevent water from running across the top to storage and
down the flues and can also collect water. The container will prevent water 
penetration to a fire in lower levels where it is needed. Rack or flue collapse 
can also occur if too much water is collected. Consideration should be given to 
the potential degree of water collection possible within the container when 
applying the definition of an open-top container. The following  conditions 
should be considered:
(1) Small openings at the top of containers containing such items as fresh 
produce are quite common and should not be considered as an open-top container.
(2) Arrangements that include open-top containers that are all located on the 
bottom tier of rack storage do not prevent penetration of water and should not 
be considered an open-top container.
(3) Containers having either wire mesh siding or large uniform openings along 
the bottom perimeter of each container, such that water enters the container at 
the same flow rate and discharge evenly into the flue spaces should not be 
considered as an open-top container provided the contents of the container are 
not water absorbent and are not capable of blocking such container openings.

The protection of this type of storage is clearly not under the "practice" of a 
NICET tech following the prescribed protection guidelines of a published NFPA 
standard (White Paper developed by SFPE, NICET and NSPE) especially since the 
standard states many times that open-top containers are not covered by the 
standard. The specifying engineer might be "outside" his/her "area of 
competence" as defined by the Professional Engineering Laws and Code of Ethics 
formulated by the state or commonwealth they are "practicing" in.

Just my two cents and interpretation by a NICET Tech when NFPA 13 specifically 
states that the protection of open top containers are outside the scope of 
specific NFPA 13 chapters could be considered the practice of engineering and 
subject their company to an E & O exposure not covered by the company's 
insurance policy.

Why expose yourself and your company to such an exposure.

Have a fire safe day!

Regards

Jim



Davidson Associates

Fire Protection Engineering                                                     
                                                                                
       P. O. Box 4002
Code Consultants                                                                
                                                                                
Greenville, DE  19807
                                                                                
                                                                                
                       (302) 994-9500
                                                                                
                                                                                
                Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 11:31 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: HDPE Plastic Bin Box Storage

Jeff:

I appreciate your "caution" on this and perhaps I am overreaching here. But in 
my view, I'm just trying to correctly interpret the commodity classification 
and arrangement as it relates to the storage provisions of  NFPA-13, which 
should fall under my practice. In fact, I am working with a specifying engineer 
on this who is just as baffled by the insurance underwriter's concerns as I am. 
The problem is, this arrangement is not "specifically" addressed in 13. Is this 
bin box storage, (it's not cardboard or corrugated) or open container storage? 
From everything that I can tell, if it meet the OHII curve, that should be the 
governing requirement.

Thanks,

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeff Hewitt
Sent: Thursday, December 8, 2016 11:03 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: HDPE Plastic Bin Box Storage

John,

I'm writing off on the forum because I don't want to stir up a hornets nest.

Isn't this an engineering decision, not a NICET SET decision?

I'm just saying, why would you want to take that liability as a NICET SET, and 
also potentially violate your NICET Certification by practicing engineering.

Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

      [cid:[email protected]]
American Fire Protection, Inc.
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

          
[http://secure-web.cisco.com/1jNepulB8CK-Tb5bV_VkuxvOr42evx8jjIVHbd_OzqsGN5nCYVlQGlKx-CLJYABI0CH2kNjrZqdh4oA6sGfI2xDlvlCs3lXNk7S0lgLlfPGw3T-WsqbLy3aulDF4GO3vjMrC3VQJsy_Rl5AieZLBABQ0wIYjMq_OLF1j1-DbyTguFXznPNeemLlsSQecQLrwBGS76U4zKbOOKPVE1oMYnVNZZfeY-Tlg_S4WDedKB3K8lEpVMcO6030heu80gJiLeS8f5JsD_IPdvvLIKTsNpEO51gXpogJ1UjVDPIOJ0okWCll1lWrQKLUrUSnE2SJICBZgta0Z7GLyyZ921I96OCCslqwnud3wR2CwORK1_n0AS_nf-1Uaa_bvVIVBGrwVm7m0HTFMJkXZCAfVxP5ZUe3AM8vW9R5T9Md6MFZXjMBFX7-KaoS0-iBvX8D8mL5qKZBS3D96c_z-I_zd7dI3PxvtEs2X1E_XEf_6k2z1lgf4/http%3A%2F%2Fwww.sfpe.org%2Fresource%2Fresmgr%2FMember_Logos%2FProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Thursday, December 08, 2016 9:43 AM
To: 
[email protected]<mailto:[email protected]>
Subject: HDPE Plastic Bin Box Storage

Hello All!

I am working with a truck parts supplier who has moved into an existing 
warehouse and I am providing a design study to them on the existing system.

Pertinent Facts:

6"x6"x2" Grid with K-8.0 Upright Heads fed by a pump. Pipe is at 25' AFF.
Metal truck parts storage in HDPE Plastic Bin Boxes stored no higher than 10'
Existing system with 500 GPM hose calcs to .60 GPM / 3,000.
Tokyo Mutual Insurance

Personally I think the system provides adequate protection for the storage 
configuration. In fact it is MORE than sufficient according to NFPA 13, Ch 14.  
However the insurance company is maintaining that the plastic bin storage boxes 
represent an additional hazard. This is a new experience for me. My contention 
is that the Bin Boxes, even though they are made of HDPE Plastic, do not 
represent an increase to the commodity classification because of their higher 
flash point. (which is information I can't seem to find right now)

Is there a fire test out there that indicates these bin boxes represent an 
increased hazard?

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to