From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mark Phillips Sent: January-23-17 4:11 PM To: [email protected] Subject: RE: QR STANDARD SPRAY SPRINKLERS NFPA 13 2013 ED 8.6.5.2.1.3 (A) From: Sprinklerforum [mailto:[email protected]] On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Monday, January 23, 2017 4:06 PM To: [email protected] Subject: RE: QR STANDARD SPRAY SPRINKLERS CAN YOU REFERENCE A CODE FOR ME? From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mark Phillips Sent: January-23-17 4:05 PM To: [email protected] Subject: RE: QR STANDARD SPRAY SPRINKLERS Three times rule applies to the fan housing unit (motor) From: Sprinklerforum [mailto:[email protected]] On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Monday, January 23, 2017 3:56 PM To: [email protected] Subject: QR STANDARD SPRAY SPRINKLERS I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A CEILING FAN WITH RESIDENTIAL HEADS I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R. PENDENT OR CONCEALED HEADS. CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE? THANKS