NFPA 13 2013 ED 8.6.5.2.1.3 (A)

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 4:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: QR STANDARD SPRAY SPRINKLERS

CAN YOU REFERENCE A CODE FOR ME?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: January-23-17 4:05 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: QR STANDARD SPRAY SPRINKLERS

Three times rule applies to the fan housing unit (motor)

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 3:56 PM
To: 
[email protected]<mailto:[email protected]>
Subject: QR STANDARD SPRAY SPRINKLERS

I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A 
CEILING FAN WITH RESIDENTIAL HEADS

I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R. 
PENDENT OR CONCEALED HEADS.

CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE?