For a twist: Yes, you would follow 3x rule. However, it is likely light hazard 
with ceiling fan. So, since it is non-structural, do you have to follow it? 

 

I think prudent design is to be the 3x away with QR sprinklers. However, it 
could be ignored since it is non-structural. 

 

I typically see residential or ex cov sprinklers in these situations and that 
forces you to the 4x rule. Plus the allowance for non-structural is only for 
standard spray sprinklers. 

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook:  
<https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

 

Sent from my iPhone


On Jan 23, 2017, at 2:10 PM, Mark Phillips <[email protected]> wrote:

NFPA 13 2013 ED 8.6.5.2.1.3 (A)

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 4:06 PM
To: [email protected]
Subject: RE: QR STANDARD SPRAY SPRINKLERS

 

CAN YOU REFERENCE A CODE FOR ME?

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Phillips
Sent: January-23-17 4:05 PM
To: [email protected]
Subject: RE: QR STANDARD SPRAY SPRINKLERS

 

Three times rule applies to the fan housing unit (motor)

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 23, 2017 3:56 PM
To: [email protected]
Subject: QR STANDARD SPRAY SPRINKLERS

 

I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A 
CEILING FAN WITH RESIDENTIAL HEADS

 

I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R. 
PENDENT OR CONCEALED HEADS.

 

CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE?

 

THANKS

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to