For a twist: Yes, you would follow 3x rule. However, it is likely light hazard with ceiling fan. So, since it is non-structural, do you have to follow it?
I think prudent design is to be the 3x away with QR sprinklers. However, it could be ignored since it is non-structural. I typically see residential or ex cov sprinklers in these situations and that forces you to the 4x rule. Plus the allowance for non-structural is only for standard spray sprinklers. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Jan 23, 2017, at 2:10 PM, Mark Phillips <[email protected]> wrote: > > NFPA 13 2013 ED 8.6.5.2.1.3 (A) > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Trillium Fire Sprinkler Design Inc. > Sent: Monday, January 23, 2017 4:06 PM > To: [email protected] > Subject: RE: QR STANDARD SPRAY SPRINKLERS > > CAN YOU REFERENCE A CODE FOR ME? > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Mark Phillips > Sent: January-23-17 4:05 PM > To: [email protected] > Subject: RE: QR STANDARD SPRAY SPRINKLERS > > Three times rule applies to the fan housing unit (motor) > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Trillium Fire Sprinkler Design Inc. > Sent: Monday, January 23, 2017 3:56 PM > To: [email protected] > Subject: QR STANDARD SPRAY SPRINKLERS > > I KNOW FOR 13R YOU NEED TO BE A MINIMUM OF 3'-0" AWAY FROM THE CENTER OF A > CEILING FAN WITH RESIDENTIAL HEADS > > I CANNOT FIND WHERE THE SAME APPLIES FOR A 13 SYSTEM USING STANDARD Q.R. > PENDENT OR CONCEALED HEADS. > > CAN SOMEONE VERIFY OR EDUCATED ME ON THIS PLEASE? > > THANKS > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org