Roland,

If I remember correctly there was an analysis based on OSHA required “ARC” 
Flash analysis  of a typical 440 volt fire pump controller. The analysis  found 
that even with the highest level of PPE the person doing the measurements in 
the controller would need to be at such a distance from the controller that 
they would be outside the pump room. This is something I heard from a pump 
controller rep. As a sprinkler contractor I would be very careful measuring 
voltage and amps in an electric fire pump controller.

I also thought that NFPA 25 is modifying the language in the fire pump 
controller section of the standard to eliminate the requirement for the 
sprinkler inspector to measure the voltage and amps.

If the fire pump is tested annually the master electrician can be measuring the 
Amps and Voltage during the test.

Just my 2 cents !

Have a fire safe day!

Jim Davidson

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Monday, March 27, 2017 12:26 PM
To: [email protected]
Subject: Re: Another NFPA 25 Question - Controllers

Speaking of owner’s don’t care, does any think that NFPA 25 is completely out 
of control regarding pumps?


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives



On Mar 27, 2017, at 8:51 AM, John Irwin 
<[email protected]<mailto:[email protected]>> 
wrote:

I love the sentiment. But that’s a lot of up-selling when it comes to selling 
an inspection. We’re still competing with bottom feeders. And most property 
managers just don’t care.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to