A few years ago we changed our procedure so that if the controller does not
have a digital read out of amps and volts, we would not provide it.  We
will not open controllers; not worth the risk.  We have told owners and
their insurance companies that we would be happy to provide a qualified
electrician on a T & M basis if those numbers are required.  No one has
taken us up on it in the past 3 or 4 years.

*Jay Stough*
NICET IV LAYOUT
NICET III ITM

On Mon, Mar 27, 2017 at 3:41 PM, Bruce Verhei <[email protected]> wrote:

> As a municipal fire inspector I always made sure I stood well back when
> the controller door was open. Flash burns are ugly. It's not like getting a
> simple broken arm or something.
>
> But I'm usually witnessing acceptance test.
>
> Most annual tests do include amps on each leg.
>
> Some have lead this discussion away from what is code towards how should
> this be addressed. This is good in this case.
>
> I'd bet few NFPA 25 inspectors are NFPA 70E whizzes.
>
> Diesel controllers. Not the same at all.
>
> Best
>
> Bruce Verhei
>
> On Mar 27, 2017, at 09:14, John Irwin <[email protected]>
> wrote:
>
> Great answer.
>
>
>
> *John Irwin - CET*
>
> *Division Manager – Fire Sprinklers*
>
> *Critical System Solutions, LLC*
>
>
> *Licence Number: FPC16-000053*Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
> <image003.png>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Jeremy
> Blocker
> *Sent:* Monday, March 27, 2017 12:06 PM
> *To:* [email protected]
> *Subject:* Re: Another NFPA 25 Question - Controllers
>
>
>
> The only ones we do in house are diesel drivers.  This decision was only
> made when the insurance agent explained everything we would need to do to
> cover our rear.  Also we found out that local licensing requires a master
> electrician be the one to touch high voltage.  So the scenario presented to
> us was that my inspector is hurt by electrical equipment. The attorneys
> would as for his license as an electrician, copies of his safety training
> that we provided. If we couldn't show all this we were a sitting duck in
> court.
>
> JJ
>
> Sent from my iPhone 6
>
>
> On Mar 27, 2017, at 9:52 AM, John Irwin <JIrwin@
> criticalsystemsolutions.com> wrote:
>
> You say 440 volt … So you do the 208v yourself?
>
>
>
> *John Irwin - CET*
>
> *Division Manager – Fire Sprinklers*
>
> *Critical System Solutions, LLC*
>
>
> *Licence Number: FPC16-000053*Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
> <image003.png>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Jeremy
> Blocker
> *Sent:* Monday, March 27, 2017 11:43 AM
> *To:* [email protected]
> *Subject:* Re: Another NFPA 25 Question - Controllers
>
>
>
> The easiest solution we found when faced with this very problem was to
> call in the experts.  When we asked our insurance agent about this we
> discovered that we could end up needing to change our policy to cover high
> voltage exposure.   So we now use manufacturers recommended pump service
> companies to perform the test.   This not only keeps us away from the 440
> volt 3 phase power but it also allows the specialist to find issues that
> the average sprinkler inspector would not notice.  Our reports are carrying
> more weight now as well since a P.E. signs the pump report.
>
> JJ
>
> Sent from my iPhone 6
>
>
> On Mar 27, 2017, at 9:25 AM, Matthew J Willis <[email protected]>
> wrote:
>
> IS voltage a required item on the report? Along with amps?
>
>
>
> I always had the PPE and shook hands within..
>
>
>
> R/
>
> Matt
>
>
>
> *Matthew J. Willis*
>
> *Project Manager*
>
> *Rapid Fire Protection Inc.* <http://rapidfireinc.com/>
>
> *1530 Samco Road*
>
> *Rapid City, SD 57702*
>
> *Office-605.348.2342 <(605)%20348-2342>*
>
> *Direct Line-605.593.5063 <(605)%20593-5063>*
>
> *Cell-605.391.2733 <(605)%20391-2733>*
>
> *Fax:-605.348.0108 <(605)%20348-0108>*
>
>
>
> <image001.png>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Roland
> Huggins
> *Sent:* Monday, March 27, 2017 9:23 AM
> *To:* [email protected]
> *Subject:* Re: Another NFPA 25 Question - Controllers
>
>
>
> There is a TIA to NFPA 25 effectively saying stay the hell out of it.
> We’ll see where it goes but it makes sense considering the hazard.  What do
> our pump inspectors herein think?
>
>
>
> Roland
>
>
>
>
>
> Roland Huggins, PE - Senior VP Engineering
>
> American Fire Sprinkler Assn.
>
> Dallas, TX
>
> http://www.firesprinkler.org
>
>
>
> Fire Sprinklers Saves Lives
>
>
>
>
>
>
>
> On Mar 27, 2017, at 4:32 AM, John Denhardt <[email protected]>
> wrote:
>
>
>
> My personal opinion - no.
>
> John August Denhardt, P.E.
>
> Strickland Fire Protection
>
>
> On Mar 27, 2017, at 6:34 AM, John Irwin <JIrwin@
> criticalsystemsolutions.com> wrote:
>
> What are an inspector’s responsibilities when it comes to opening up a
> fire pump controller? One of our inspector’s wants me to buy him some PPE
> so he can comfortably open up the fire pump controller. I am certainly not
> opposed to this but I have talked to a number of inspectors at other
> companies who say if there isn’t an external meter on the cabinet, the
> voltage isn’t getting recorded. Should sprinkler inspectors even be in the
> cabinet?
>
>
>
>
>
>
>
>
>
> *John Irwin - CET*
>
> *Division Manager – Fire Sprinklers *
>
> *Critical System Solutions, LLC*
>
>
> *License Number: FPC16-000053*2830 Scherer Drive, Suite 300
> St. Petersburg, FL  33716
> Office: 727.209.5122 <(727)%20209-5122>
>
> Fax:      727.209.5126 <(727)%20209-5126>
>
> Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
> <image003.png>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> <image003.png>_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to