Remember friends that the text Travis quoted was _*added*_ in the 2010 edition of -13. Dewayne's inquiry began with a note that his project was governed by the 2007. Still, the value for dry system water delivery time of 15 seconds for residential occupancies was the first item in Table 7.2.3.6.1.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 04/06/2017 8:36 AM, Travis Mack, SET wrote:

It can be R or I occupancy. It doesn't matter. It is the fact you are protecting a dwelling unit with a dry pipe system.

7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of any occupancy, the sprinklers in the dwelling unit shall have a maximum water delivery time of 15 seconds to the
single most remote sprinkler.

It seems like you have 15 seconds regardless. Now, if you have a dry pipe valve on the first floor and I believe you said these were on the 5th floor, it seems quite unlikely you will get 15 seconds. My suggestion is to find a way to supply these sprinklers in the dwelling units from a wet pipe system.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via:https://www.hightail.com/u/MFPDesign LinkedIn:https://www.linkedin.com/in/travismack
On 4/6/2017 8:16 AM, Dewayne Martinez wrote:

That was one of my concerns also. R-2 floor occupancy, calculating it per light hazard but using residential heads. If the R-2 occupancy is what would dictate the 15sec delivery time then it wouldn’t matter what type of heads I used in the residential areas.

*From:*Sprinklerforum [mailto:[email protected] <mailto:[email protected]>] *On Behalf Of *Travis Mack
*Sent:* Thursday, April 06, 2017 8:58 AM
*To:* [email protected] <mailto:[email protected]>
*Subject:* Re: NFPA 13 dry system - residential sprinklers

Double check delivery times. I think you need a 15 second delivery time in residential areas.

Travis Mack, SET

MFP Design, LLC

"Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign

Sent from my iPhone


On Apr 6, 2017, at 6:31 AM, Dewayne Martinez <[email protected] <mailto:[email protected]>> wrote:

    The dry portion below the attic was laid out at max 15x15 spacing
    with the
    lines at 15ft above the floor.  The way the rooms layout there
    are long
    runs with 8ft ceilings so I was going to drop down once to feed
    all these
    rooms with one line but I still need to size it.  This reviewer
    will still
    make us calculate the residential build out portion.  I can get
    by with a
    1 1/4" line calculating  4 heads.

    -----Original Message-----
    From: Mark Phillips [mailto:[email protected]]
    Sent: Thursday, April 06, 2017 8:17 AM
    To: [email protected]
    <mailto:[email protected]>
    Cc: [email protected]
    <mailto:[email protected]>
    Subject: Re: NFPA 13 dry system - residential sprinklers

    If I'm understanding
    The roof system is unchanged and your adding a lower supply to be
    rooms.

    Use standard qr heads and same pipe sizes

    The roof is still most demanding

    Sent from my Verizon 4G LTE Droid
    On Apr 6, 2017 9:14 AM, Dewayne Martinez
    <[email protected]
    <mailto:[email protected]>>
    wrote:
    NFPA 13 (07ed)

    I have an existing 5th floor shell space that is installed as a light
    hazard dry system that has pipe in the shell space and in the
    attic.  They
    are turning this floor into a dormitory (R-2).
    1)Can I use listed residential heads on return bends and only
    pick up 4
    heads per 11.3.1.1 or will I need to pick up 1950SF? What if
    there are
    incidental areas such as a laundry room, ect. in the same areas
    as the
    dorm rooms?
    2)What would be the required trip time be per Table 7.2.3.6.1?
     15sec for
    residential or 60sec for light hazard?

    Thanks,
    Dewayne Martinez
    Fire Protection Design Manager

    TOTAL Mechanical
    Building Integrity
    W234 N2830 Paul Rd.
    Pewaukee, WI  53072
    [email protected]
    
<mailto:[email protected]><mailto:[email protected]>
    Ph:  262-522-7110
    Cell: 414-406-5208
    http://www.total-mechanical.com/

    [cid:[email protected]]
    [cid:[email protected]]
    [cid:[email protected]]  [Top Workplaces 2015]

    TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
    _______________________________________________
    Sprinklerforum mailing list
    [email protected]
    <mailto:[email protected]>
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to