Pete,
I certainly agree, which is why I was delighted to see that the 15 second delivery time was present in the earlier edition, so it was applicable under that standard as well.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 04/06/2017 5:36 PM, Pete Schwab wrote:

Ken

Even though an earlier edition governs, standard of care from a liability issue would dictate not ignoring the 15 second requirement.

Just my opinion

Pete

Peter Schwab

VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.

222 Capitol Court

Ocoee, Fl 34761

*Mobile: (407) 468-8248*

Direct: (407) 877-5570

Fax: (407) 656-8026

www.waynefire.com <http://www.waynefire.com/>

Description: cid:[email protected]

*/I sleep in a sprinklered home, do you? /*

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Parsley Consulting
*Sent:* Thursday, April 06, 2017 12:02 PM
*To:* [email protected]
*Subject:* Re: NFPA 13 dry system - residential sprinklers

Remember friends that the text Travis quoted was *_added_* in the 2010 edition of -13. Dewayne's inquiry began with a note that his project was governed by the 2007. Still, the value for dry system water delivery time of 15 seconds for residential occupancies was the first item in Table 7.2.3.6.1.

*Ken Wagoner, SET
**Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
**Phone 760-745-6181
**Visit our website <http://www.parsleyconsulting.com/> *

On 04/06/2017 8:36 AM, Travis Mack, SET wrote:

    It can be R or I occupancy.  It doesn't matter.  It is the fact
    you are protecting a dwelling unit with a dry pipe system.

    7.2.3.6.3 For dry pipe systems protecting dwelling unit portions
    of any occupancy, the sprinklers in the dwelling unit shall have a
    maximum water delivery time of 15 seconds to the
    single most remote sprinkler.

    It seems like you have 15 seconds regardless.  Now, if you have a
    dry pipe valve on the first floor and I believe you said these
    were on the 5th floor, it seems quite unlikely you will get 15
    seconds.  My suggestion is to find a way to supply these
    sprinklers in the dwelling units from a wet pipe system.

    Travis Mack, SET

    MFP Design, LLC

    2508 E Lodgepole Drive

    Gilbert, AZ 85298

    480-505-9271

    fax: 866-430-6107

    email:[email protected] <mailto:email:[email protected]>

    http://www.mfpdesign.com

    https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:https://www.hightail.com/u/MFPDesign
    LinkedIn:https://www.linkedin.com/in/travismack

    On 4/6/2017 8:16 AM, Dewayne Martinez wrote:

        That was one of my concerns also. R-2 floor occupancy,
calculating it per light hazard but using residential heads. If the R-2 occupancy is what would dictate the 15sec delivery
        time then it wouldn’t matter what type of heads I used in the
        residential areas.

        *From:*Sprinklerforum
        [mailto:[email protected]
        <mailto:[email protected]>] *On
        Behalf Of *Travis Mack
        *Sent:* Thursday, April 06, 2017 8:58 AM
        *To:* [email protected]
        <mailto:[email protected]>
        *Subject:* Re: NFPA 13 dry system - residential sprinklers

        Double check delivery times. I think you need a 15 second
        delivery time in residential areas.

        Travis Mack, SET

        MFP Design, LLC

        "Follow" us on Facebook:
        https://www.facebook.com/pages/MFP-Design-LLC/92218417692

        Send large files to MFP Design via:

        https://www.hightail.com/u/MFPDesign

        Sent from my iPhone


        On Apr 6, 2017, at 6:31 AM, Dewayne Martinez
        <[email protected]
        <mailto:[email protected]>> wrote:

            The dry portion below the attic was laid out at max 15x15
            spacing with the
            lines at 15ft above the floor.  The way the rooms layout
            there are long
            runs with 8ft ceilings so I was going to drop down once to
            feed all these
            rooms with one line but I still need to size it.  This
            reviewer will still
            make us calculate the residential build out portion. I can
            get by with a
            1 1/4" line calculating  4 heads.

            -----Original Message-----
            From: Mark Phillips [mailto:[email protected]]
            Sent: Thursday, April 06, 2017 8:17 AM
            To: [email protected]
            <mailto:[email protected]>
            Cc: [email protected]
            <mailto:[email protected]>
            Subject: Re: NFPA 13 dry system - residential sprinklers

            If I'm understanding
            The roof system is unchanged and your adding a lower
            supply to be rooms.

            Use standard qr heads and same pipe sizes

            The roof is still most demanding

            Sent from my Verizon 4G LTE Droid
            On Apr 6, 2017 9:14 AM, Dewayne Martinez
            <[email protected]
            <mailto:[email protected]>>
            wrote:
            NFPA 13 (07ed)

            I have an existing 5th floor shell space that is installed
            as a light
            hazard dry system that has pipe in the shell space and in
            the attic.  They
            are turning this floor into a dormitory (R-2).
            1)Can I use listed residential heads on return bends and
            only pick up 4
            heads per 11.3.1.1 or will I need to pick up 1950SF? What
            if there are
            incidental areas such as a laundry room, ect. in the same
            areas as the
            dorm rooms?
            2)What would be the required trip time be per Table
            7.2.3.6.1?  15sec for
            residential or 60sec for light hazard?

            Thanks,
            Dewayne Martinez
            Fire Protection Design Manager

            TOTAL Mechanical
            Building Integrity
            W234 N2830 Paul Rd.
            Pewaukee, WI  53072
            [email protected]
            
<mailto:[email protected]><mailto:[email protected]>
            Ph:  262-522-7110
            Cell: 414-406-5208
            http://www.total-mechanical.com/

            [cid:[email protected]]
            [cid:[email protected]]
            [cid:[email protected]]  [Top Workplaces 2015]

            TOTAL Mechanical voted "Top Workplace" for a 4th
            consecutive year.
            _______________________________________________
            Sprinklerforum mailing list
            [email protected]
            <mailto:[email protected]>
            
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




        _______________________________________________

        Sprinklerforum mailing list

        [email protected]
        <mailto:[email protected]>

        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





    _______________________________________________

    Sprinklerforum mailing list

    [email protected]
    <mailto:[email protected]>

    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to