Pete,
I certainly agree, which is why I was delighted to see that the 15
second delivery time was present in the earlier edition, so it was
applicable under that standard as well.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 04/06/2017 5:36 PM, Pete Schwab wrote:
Ken
Even though an earlier edition governs, standard of care from a
liability issue would dictate not ignoring the 15 second requirement.
Just my opinion
Pete
Peter Schwab
VP of Purchasing and Engineering technologies
Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761
*Mobile: (407) 468-8248*
Direct: (407) 877-5570
Fax: (407) 656-8026
www.waynefire.com <http://www.waynefire.com/>
Description: cid:[email protected]
*/I sleep in a sprinklered home, do you? /*
*From:*Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Parsley Consulting
*Sent:* Thursday, April 06, 2017 12:02 PM
*To:* [email protected]
*Subject:* Re: NFPA 13 dry system - residential sprinklers
Remember friends that the text Travis quoted was *_added_* in the 2010
edition of -13. Dewayne's inquiry began with a note that his project
was governed by the 2007. Still, the value for dry system water
delivery time of 15 seconds for residential occupancies was the first
item in Table 7.2.3.6.1.
*Ken Wagoner, SET
**Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
**Phone 760-745-6181
**Visit our website <http://www.parsleyconsulting.com/> *
On 04/06/2017 8:36 AM, Travis Mack, SET wrote:
It can be R or I occupancy. It doesn't matter. It is the fact
you are protecting a dwelling unit with a dry pipe system.
7.2.3.6.3 For dry pipe systems protecting dwelling unit portions
of any occupancy, the sprinklers in the dwelling unit shall have a
maximum water delivery time of 15 seconds to the
single most remote sprinkler.
It seems like you have 15 seconds regardless. Now, if you have a
dry pipe valve on the first floor and I believe you said these
were on the 5th floor, it seems quite unlikely you will get 15
seconds. My suggestion is to find a way to supply these
sprinklers in the dwelling units from a wet pipe system.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] <mailto:email:[email protected]>
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via:https://www.hightail.com/u/MFPDesign
LinkedIn:https://www.linkedin.com/in/travismack
On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
That was one of my concerns also. R-2 floor occupancy,
calculating it per light hazard but using residential heads.
If the R-2 occupancy is what would dictate the 15sec delivery
time then it wouldn’t matter what type of heads I used in the
residential areas.
*From:*Sprinklerforum
[mailto:[email protected]
<mailto:[email protected]>] *On
Behalf Of *Travis Mack
*Sent:* Thursday, April 06, 2017 8:58 AM
*To:* [email protected]
<mailto:[email protected]>
*Subject:* Re: NFPA 13 dry system - residential sprinklers
Double check delivery times. I think you need a 15 second
delivery time in residential areas.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign
Sent from my iPhone
On Apr 6, 2017, at 6:31 AM, Dewayne Martinez
<[email protected]
<mailto:[email protected]>> wrote:
The dry portion below the attic was laid out at max 15x15
spacing with the
lines at 15ft above the floor. The way the rooms layout
there are long
runs with 8ft ceilings so I was going to drop down once to
feed all these
rooms with one line but I still need to size it. This
reviewer will still
make us calculate the residential build out portion. I can
get by with a
1 1/4" line calculating 4 heads.
-----Original Message-----
From: Mark Phillips [mailto:[email protected]]
Sent: Thursday, April 06, 2017 8:17 AM
To: [email protected]
<mailto:[email protected]>
Cc: [email protected]
<mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers
If I'm understanding
The roof system is unchanged and your adding a lower
supply to be rooms.
Use standard qr heads and same pipe sizes
The roof is still most demanding
Sent from my Verizon 4G LTE Droid
On Apr 6, 2017 9:14 AM, Dewayne Martinez
<[email protected]
<mailto:[email protected]>>
wrote:
NFPA 13 (07ed)
I have an existing 5th floor shell space that is installed
as a light
hazard dry system that has pipe in the shell space and in
the attic. They
are turning this floor into a dormitory (R-2).
1)Can I use listed residential heads on return bends and
only pick up 4
heads per 11.3.1.1 or will I need to pick up 1950SF? What
if there are
incidental areas such as a laundry room, ect. in the same
areas as the
dorm rooms?
2)What would be the required trip time be per Table
7.2.3.6.1? 15sec for
residential or 60sec for light hazard?
Thanks,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
[email protected]
<mailto:[email protected]><mailto:[email protected]>
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/
[cid:[email protected]]
[cid:[email protected]]
[cid:[email protected]] [Top Workplaces 2015]
TOTAL Mechanical voted "Top Workplace" for a 4th
consecutive year.
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org