I have appreciated the many opportunities to learn much from reading the 
exchanges on this forum.
Today I am inclined to add this comment:
"They are turning this floor into a dormitory (R-2)". I believe that the change 
of occupancy classification / use would dictate compliance with the code/ 
standards that are current to the time of change, which if I understand this 
thread is the present. The recommendation to install a wet system seems most 
appropriate.
One man's opinion.

Ed Foster
Fire Marshal
Fire Prevention Bureau
Carpinteria-Summerland Fire District
(805) 566-2451
[cid:82df1ca92855c9c2623baa3ddf8c0acda8677ac1@zimbra]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Thursday, April 06, 2017 9:02 AM
To: [email protected]
Subject: Re: NFPA 13 dry system - residential sprinklers

Remember friends that the text Travis quoted was added in the 2010 edition of 
-13.  Dewayne's inquiry began with a note that his project was governed by the 
2007.  Still, the value for dry system water delivery time of 15 seconds for 
residential occupancies was the first item in Table 7.2.3.6.1.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 04/06/2017 8:36 AM, Travis Mack, SET wrote:

It can be R or I occupancy.  It doesn't matter.  It is the fact you are 
protecting a dwelling unit with a dry pipe system.

7.2.3.6.3 For dry pipe systems protecting dwelling unit portions of any 
occupancy, the sprinklers in the dwelling unit shall have a maximum water 
delivery time of 15 seconds to the
single most remote sprinkler.

It seems like you have 15 seconds regardless.  Now, if you have a dry pipe 
valve on the first floor and I believe you said these were on the 5th floor, it 
seems quite unlikely you will get 15 seconds.  My suggestion is to find a way 
to supply these sprinklers in the dwelling units from a wet pipe system.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:[email protected]<mailto:email:[email protected]>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 4/6/2017 8:16 AM, Dewayne Martinez wrote:
That was one of my concerns also. R-2 floor occupancy, calculating it per light 
hazard but using residential heads.  If the R-2 occupancy is what would dictate 
the 15sec delivery time then it wouldn't matter what type of heads I used in 
the residential areas.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Travis Mack
Sent: Thursday, April 06, 2017 8:58 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers

Double check delivery times. I think you need a 15 second delivery time in 
residential areas.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 6, 2017, at 6:31 AM, Dewayne Martinez 
<[email protected]<mailto:[email protected]>> wrote:
The dry portion below the attic was laid out at max 15x15 spacing with the
lines at 15ft above the floor.  The way the rooms layout there are long
runs with 8ft ceilings so I was going to drop down once to feed all these
rooms with one line but I still need to size it.  This reviewer will still
make us calculate the residential build out portion.  I can get by with a
1 1/4" line calculating  4 heads.

-----Original Message-----
From: Mark Phillips [mailto:[email protected]]
Sent: Thursday, April 06, 2017 8:17 AM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: Re: NFPA 13 dry system - residential sprinklers

If I'm understanding
The roof system is unchanged and your adding a lower supply to be rooms.

Use standard qr heads and same pipe sizes

The roof is still most demanding

Sent from my Verizon 4G LTE Droid
On Apr 6, 2017 9:14 AM, Dewayne Martinez 
<[email protected]<mailto:[email protected]>>
wrote:
NFPA 13 (07ed)

I have an existing 5th floor shell space that is installed as a light
hazard dry system that has pipe in the shell space and in the attic.  They
are turning this floor into a dormitory (R-2).
1)Can I use listed residential heads on return bends and only pick up 4
heads per 11.3.1.1 or will I need to pick up 1950SF?  What if there are
incidental areas such as a laundry room, ect. in the same areas as the
dorm rooms?
2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for
residential or 60sec for light hazard?

Thanks,
Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]><mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[cid:[email protected]] [cid:[email protected]]
[cid:[email protected]]  [Top Workplaces 2015]

TOTAL Mechanical voted "Top Workplace" for a 4th consecutive year.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to