A couple of things to consider:

-        Section 8.4.5.2 – can’t use residential sprinks on a dry system unless 
specifically listed for dry systems.

-        Section 8.3.4.1(2) – Unless the pipe is galvanized or otherwise 
corrosion resistant, minimum K-factor is 5.6.  

 

So you’ll need a residential sprink that is listed for dry systems and is K5.6 
or greater.

 

Ed Kramer

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Thursday, April 06, 2017 8:13 AM
To: [email protected]
Cc: [email protected]
Subject: NFPA 13 dry system - residential sprinklers

 

NFPA 13 (07ed)

 

I have an existing 5th floor shell space that is installed as a light hazard 
dry system that has pipe in the shell space and in the attic.  They are turning 
this floor into a dormitory (R-2).

1)Can I use listed residential heads on return bends and only pick up 4 heads 
per 11.3.1.1 or will I need to pick up 1950SF?  What if there are incidental 
areas such as a laundry room, ect. in the same areas as the dorm rooms?

2)What would be the required trip time be per Table 7.2.3.6.1?  15sec for 
residential or 60sec for light hazard?    

 