By the way the Engineer of Record has called for Light Hazard Occupancy for the Flight Simulator area Roof Line Coverage.

I am going to question that provided I can get information about the simulator equipment. In reviewing NFPA 13 & FM Data Sheet 7-3 sprinkler protection under the Cabs will also be required.


Regards,

G. Tim Stone

G. Tim Stone Consulting, LLC

117 Old Stage Rd.

Essex Junction, VT. 05452

Cell: (802) 373-0638

[email protected]

On September 20, 2017 at 10:21 AM [email protected] wrote:

 
If this is a military project, do they have a spec on flight simulators?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT


On Sep 20, 2017 at 9:59 AM, <Tim Stone> wrote:

US Air force project. F35 fight simulators, 4 of them inside one building.


 Regards,

G. Tim Stone

G. Tim Stone Consulting, LLC

117 Old Stage Rd.

Essex Junction, VT. 05452

Cell: (802) 373-0638

[email protected]

On September 20, 2017 at 9:29 AM Matt Grise <[email protected]> wrote:

What is in the simulators? Could there be a shielded fire in there?

 

Matt

 

 

From: Sprinklerforum [mailto:[email protected]] On Behalf Of Prahl, Craig/GVL
Sent: Wednesday, September 20, 2017 8:27 AM
To: [email protected]
Subject: RE: Flight Simulator Bldg

 

Are these servo motor articulated or use hydraulic fluids?

 

If there are no hydraulic fluids or other contributing hazards, the building may be able to classified as an F-2 occupancy and no sprinklers required.

 

You might also investigate the possibility of a water mist or hybrid water mist system in lieu of sprinklers for such an occupancy but that will take some analysis and engineering work to determine suitability or viability of the option.

 


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

 

From: Sprinklerforum [mailto:[email protected]] On Behalf Of TIM STONE
Sent: Wednesday, September 20, 2017 9:23 AM
To: [email protected]
Subject: Fwd: Flight Simulator Bldg [EXTERNAL]

 

What occupancy should be considered?

Steel building, 25' high with Flight Simulators inside. Engineer has asked that no sprinklers be installed directly over simulators which are about 22' in diameter. I need to use extended coverage. Occupancy not specified. I am leaning toward Ordinary Hazard 1 as minimum.

Am I on the right track or could I consider Light Hazard?

Cheers,

G. Tim Stone

G. Tim Stone Consulting, LLC

117 Old Stage Rd.

Essex Junction, VT. 05452

Cell: (802) 373-0638

[email protected]


 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to