Ron,
Thank you for the information. The engineer of record had some information on the simulators, Fully electric, He assured me no hydraulics and he sticking with Light Hazard Design requirement.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
117 Old Stage Rd.
Essex Junction, VT. 05452
Cell: (802) 373-0638
On September 21, 2017 at 2:32 PM "rongreenman ." <[email protected]> wrote:Might be something in here._______________________________________________On Thu, Sep 21, 2017 at 5:33 AM, TIM STONE <[email protected]> wrote:By the way the Engineer of Record has called for Light Hazard Occupancy for the Flight Simulator area Roof Line Coverage.
I am going to question that provided I can get information about the simulator equipment. In reviewing NFPA 13 & FM Data Sheet 7-3 sprinkler protection under the Cabs will also be required.
On September 20, 2017 at 10:21 AM [email protected] wrote:If this is a military project, do they have a spec on flight simulators?
Todd G Williams, PEFire Protection Design/ConsultingStonington, CT860-535-2080 (ofc)860-553-3553 (fax)860-608-4559 (cell)US Air force project. F35 fight simulators, 4 of them inside one building.
On September 20, 2017 at 9:29 AM Matt Grise <[email protected]> wrote:What is in the simulators? Could there be a shielded fire in there?
Matt
From: Sprinklerforum [mailto:sprinklerforum-
[email protected]. org] On Behalf Of Prahl, Craig/GVL
Sent: Wednesday, September 20, 2017 8:27 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Flight Simulator Bldg
Are these servo motor articulated or use hydraulic fluids?
If there are no hydraulic fluids or other contributing hazards, the building may be able to classified as an F-2 occupancy and no sprinklers required.
You might also investigate the possibility of a water mist or hybrid water mist system in lieu of sprinklers for such an occupancy but that will take some analysis and engineering work to determine suitability or viability of the option.
Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540Fax - 864.920.7129
CH2MHILL Extension 77540
[email protected]
From: Sprinklerforum [mailto:sprinklerforum-
[email protected]. org] On Behalf Of TIM STONE
Sent: Wednesday, September 20, 2017 9:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fwd: Flight Simulator Bldg [EXTERNAL]
What occupancy should be considered?
Steel building, 25' high with Flight Simulators inside. Engineer has asked that no sprinklers be installed directly over simulators which are about 22' in diameter. I need to use extended coverage. Occupancy not specified. I am leaning toward Ordinary Hazard 1 as minimum.
Am I on the right track or could I consider Light Hazard?
Cheers,
G. Tim Stone
G. Tim Stone Consulting, LLC
Cell: (802) 373-0638
_____________________________________________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/ sprinklerforum-firesprinkler. org _________________ Sprinklerforum mailing list Sprinklerforum@lists. firesprinkler.org http://lists.firesprinkler. org/listinfo.cgi/ sprinklerforum-firesprinkler. org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/ sprinklerforum-firesprinkler. org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/ sprinklerforum-firesprinkler. org
--Ron GreenmanThe Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-)
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org