I think the key word is "one" Brian.
If you can throw under it you're good. If not, and it is a soffit
along a wall AND not greater than 30" wide you can see if option b
works.
Brad
Quoting Brian Harris <[email protected]>:
Using extended coverage pendent heads & have a soffit/reveal that is
60" wide and runs the length of the wall and sticks down 3" from the
ACT. The heads are far enough away from the edge of the
soffit/reveal to through under it and reach the wall no problem. But
if I'm reading things right since this soffit/reveal is along a wall
I have to apply either 8.8.5.1.2 (b/c) NNFPA-13 2013) which would
require heads under it as well correct? Just seems like an overkill
to me.