Agreed. "Sprinklers shall be arranged to comply with ONE of the following 
arrangements:"

If you comply with the first one (beam rule) you don't have to any further.

-Kyle M

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, October 12, 2017 9:51 AM
To: [email protected]
Subject: [EXTERNAL] Re: Soffit Along a Wall

I think the key word is "one" Brian.
If you can throw under it you're good. If not, and it is a soffit along a wall 
AND not greater than 30" wide you can see if option b works.

Brad

Quoting Brian Harris <[email protected]>:

> Using extended coverage pendent heads & have a soffit/reveal that is 
> 60" wide and runs the length of the wall and sticks down 3" from the 
> ACT. The heads are far enough away from the edge of the soffit/reveal 
> to through under it and reach the wall no problem. But if I'm reading 
> things right since this soffit/reveal is along a wall I have to apply 
> either 8.8.5.1.2 (b/c) NNFPA-13 2013) which would require heads under 
> it as well correct? Just seems like an overkill to me.
>
> Brian Harris, CET
> BVS Systems Inc.
> Design Manager
> bvssystemsinc.com<http://secure-web.cisco.com/1lUoxwFfoe0WRPDmH--tETiT
> 7qZplPzpr77InTMqRabcue3TMToKHyzXp-uyErkFMAeP_M5ybhRJBTAjC3Wj764BhcSgTm
> dQtZ4Ir76BRQjIR0CM8LU8SwcQCKna8dfWm0WG3yuGpywtxRpT5R-5u_Xw5aoCx3O9Hmti
> UpmguA-NfTg3Ar0vdHj6D22_GnyPA_soy6P17AgwuYRugJkgxIMZCPxFa4X6q1PgG7UwQH
> gPaTByRJeOF2qtP16yZIWVNk95edj6iH8PcYrk3Vn-E2w/http%3A%2F%2Fbvssystemsi
> nc.com%2F>
> Phone: 704.896.9989
> Fax: 704.896.1935



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://secure-web.cisco.com/1GQJ8eelES01ZkH6I23qzr1fBlkPMjQ8W9reI924OYQbq9RYWHR8BWxyReZAr5u1QuOkqn0pWd8kFAIMJm6dw521DFLDqgkzqeogjaMx3BNvA-anhiVOIZV1DHrJ48x6PegJTiqAV8H7S0YIN0P-MZTAytppQecAbh-6SDlTXzoxisHFNNCJuZZ10FJ5-w3l9a_pcmOjroIVBP_PWF9bMJKi34Dh3fU5-3cVdZ7TUbnjY7AfKIW2nQfevO0Z-zIXACOgJq6XXLFoC3Ap8mC-dWg/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to