Basic hydraulics - not strange at all. The calc balanced to the change.



On 1/30/2018 8:25 AM, Brian Harris wrote:

I have a calculation for a dry system that is currently -2.945 psi (-19.8%) over the curve. My most demanding head is one of (2) heads on a 1” arm-over, if I change the section of pipe (7’-6” long) that feeds this head to 1-1/4” my calc changes to +24.168 psi (136.8%) under the curve. Seems fishy to me, thoughts?