So the combined flow of the 2 sprinklers on the arm-over is about 42 GPM I 
would guess? If you run that flow through 1.25" as compared to 1",  what did 
you save in that single segment, about 5 or 7 PSI? More?

I'm still at home here on the West Coast so don't have my reference books handy 
but if you were to raise the flow of all the sprinklers in a dry pipe design 
area by an arbitrary 5 to 7 PSI (or whatever the difference is), that 
additional overflow is what's driving the higher loss of the overall system.

SL

Sent from my Verizon, Samsung Galaxy smartphone


-------- Original message --------
From: Brian Harris <[email protected]>
Date: 1/30/18 6:13 AM (GMT-08:00)
To: [email protected]
Subject: RE: Is this remotely possible ??

Steve-
.20 @ 12.755psi

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, January 30, 2018 8:40 AM
To: [email protected]
Subject: Re: Is this remotely possible ??

What's the minimum end sprinkler flow?



Sent from my Verizon, Samsung Galaxy smartphone


-------- Original message --------
From: Brian Harris <[email protected]<mailto:[email protected]>>
Date: 1/30/18 5:25 AM (GMT-08:00)
To: 
[email protected]<mailto:[email protected]>
Subject: Is this remotely possible ??

I have a calculation for a dry system that is currently -2.945 psi (-19.8%) 
over the curve. My most demanding head is one of (2) heads on a 1” arm-over, if 
I change the section of pipe (7’-6” long) that feeds this head to 1-1/4” my 
calc changes to +24.168 psi (136.8%) under the curve. Seems fishy to me, 
thoughts?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to