Brian,

That happens quite often, I learned hand calcs from the Great Dell Milam back 
in 1974.


Take a look at your results and you should see the flow and pressure are both 
lower.


Mike



________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Brian Harris <[email protected]>
Sent: Tuesday, January 30, 2018 8:25 AM
To: [email protected]
Subject: Is this remotely possible ??


I have a calculation for a dry system that is currently -2.945 psi (-19.8%) 
over the curve. My most demanding head is one of (2) heads on a 1” arm-over, if 
I change the section of pipe (7’-6” long) that feeds this head to 1-1/4” my 
calc changes to +24.168 psi (136.8%) under the curve. Seems fishy to me, 
thoughts?



Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com<http://bvssystemsinc.com/>

Fire and Life Safety Contractors - BVS Systems<http://bvssystemsinc.com/>
bvssystemsinc.com
BVS Systems Inc. is the leader in fire protection system installations and 
inspections in the southeast. We are licensed, bonded and insured and perform 
work in NC ...



Phone: 704.896.9989

Fax: 704.896.1935


_______________________________________________