Ben,

You just made my head spin and green stuff started flying everywhere! Not sure 
what that was all about, but thanks for making me think.

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Wednesday, March 28, 2018 12:45 PM
To: [email protected]; [email protected]
Subject: Re: concealed space less than 6" deep

 

Bob, I see where you're coming from with this, but we've seen this in the past 
with NFPA (previously doing the 0.10 calc for residential heads referred back 
to the small room spacing rules for SSU/P heads).

Also, 8.15.1.2.3 refers only to studs and joists and distances, not distances 
between something else.

So 1.2.3 reads '...formed by studs or joists with less than 6" between the 
inside edges of the studs or joists...'

1.2.4  reads '...formed by bar joists with less than 6" between roof or floor 
deck and ceiling...'

So in 124 you are looking at the space between a floor and ceiling

125 its between the joists and the ceiling.

But in 123, you only have the distances between joists and... more joists.

This is why I hate reading too deeply into the code. Now I'm asking myself if 
123 doesn't work the way you're saying, then how do we not have to provide 
sprinkler protection inside of wood stud walls! (I thought that was a separate 
section of 8.15.1.2 but its not there that I can see now)



Brad, 11.2.3.1.4 applies to area/density and room design.





Benjamin Young

 

On Wed, Mar 28, 2018 at 2:09 PM, Bob <[email protected]> wrote:

Ken,

The figure that is cited is an example of the 6” rule using the figure from the 
double joist requirements.  Section 8.6.4.1.5.1 & 8.15.1.2.3 are two different 
scenarios.  Borrowing the idea of less than 6” as being a triggering point (no 
snowflake innuendo intended) from the other.  They are not intended to be the 
same requirement.  In my opinion.

 

Thank you,

 

Bob Knight, CET III

208-318-3057 <tel:(208)%20318-3057> 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Wednesday, March 28, 2018 12:09 PM


To: [email protected]
Subject: Re: concealed space less than 6" deep

 

Bob,

I just looked at that section, and at first glance I see what you're driving 
at.  Then I noted "See Figure 8.6.4.1.5.1",  and I looked at the figure.  It's 
describing a vertical distance between the studs, not the distance down from 
the studs to the ceiling, so I would say that does not apply to what Ben noted. 

sincerely,

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181 <tel:(760)%20745-6181> 
Visit the website <http://www.parsleyconsulting.com/>  

On 03/28/2018 9:52 AM, Bob wrote:

Ken,

While it is true that 8.15.1.2.5 deals with solid wood joist, 8.15.1.2.3 simply 
uses the terms stud or joist with no mention of solid.  This section could be 
applied to allow for the omittance of the sprinklers.  However, as Travis 
stated the 3000 sf design area (or 8 sprinklers for residential) kicks in.

 

Thank you,

 

Bob Knight, CET III

208-318-3057 <tel:(208)%20318-3057> 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Wednesday, March 28, 2018 10:46 AM
To: [email protected]
Subject: Re: concealed space less than 6" deep

 

While I don't like to disagree with my friend Travis I feel compelled to point 
out that 8.15.1.2.5 applies only to wood joist or solid wood joist 
construction.  It's also been hammered at me and many others that TJI's such as 
Ben described are not "wood joists" for NFPA 13 purposes.

My thought for the owner, Ben, is that he would not have to fill the space with 
insulation, merely from the ceiling to the bottom of the TJI, per 8.15.1.2.8, 
and follow the firestopping mandates for the channels formed by the joists.

sincerely,

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181 <tel:(760)%20745-6181> 
Visit the website <http://www.parsleyconsulting.com/>  



On 03/28/2018 9:19 AM, MFP Design, LLC wrote:

I think 8.15.1.2.5 is going to be your best bet.  The issue is that in many 
other places of the standard, composite wood joist are specifically handled 
differently than wood joist and are not considered “similar solid member 
construction.”

 

As far as the specially listed sprinklers, I think you would have to use them 
with 8.15.1.6.  This says less than 36”, which I take as from zero to 36” in 
depth.  The specially listed sprinklers have a requirement of 6” minimum clear 
space.  This gets you back to there is no sprinkler that is available to 
protect this space.  

 

I would lean back to 8.15.1.2.5 and keep sprinklers out of the space.  But, you 
will need to increase the design area to 3000 sq ft for adjacent spaces.

 

 

 

MFP_logo_F

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271 <tel:(480)%20505-9271> 

fax: 866-430-6107 <tel:(866)%20430-6107> 

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

From: Sprinklerforum  <mailto:[email protected]> 
<[email protected]> On Behalf Of Mike Hairfield
Sent: Wednesday, March 28, 2018 9:13 AM
To: [email protected]
Subject: Re: concealed space less than 6" deep

 

I was at a AFSA NFPA 13 2013 ed seminar that was given by the AFA Virginia 
Chapter

that the Great Bob Caputo was the instructor and this came up.

 

If I remember correctly he stated that sprinklers are not required, but maybe 
it was

during one of the times that doze off.

 

Mike

 

  _____  

From: Sprinklerforum <[email protected]> on behalf 
of Ben Young <[email protected]>
Sent: Wednesday, March 28, 2018 12:06 PM
To: [email protected]
Subject: concealed space less than 6" deep 

 

I feel like this has come up here before, but nothing came back when I did 
searches through the archives.

I've got a concealed space that needs sprinklers, but I don't know how I'm 
going to put them in.

(Light hazard office space under 2013 ED of 13)

 

Wood TJI construction with an ACT suspended ceiling below it.

>From top of joist to face of ceiling is only 16.5" deep

TJIs are 12" deep

How the heck do I protect this space with only a 4.5" gap that will be even 
smaller with the grid?

Owner refuses to fill space with insulation inside trusses (for the time being)

CC spec app heads not required since the space is so small anyway, but I think 
that also means I can't use CPVC, which would make hanging the pipe parallel to 
the trusses a lot easier.

Its obstructed construction, so I should be able to put pendent heads below the 
bottom edge of the TJIs, but it will be no more than 2-3 inches above the 
ceiling.

I don't even know if that will work so worst case is I need heads inside every 
truss space, right?

The salesperson is telling me to use some weird combination of 8.15.1.2.3 
(which I believe only applied to double trusses ) and 8.15.1.2.5 (which only 
applies to solid member construction and then you have 8.15.1.2.6 directly 
below it calling out TJIs)




This definitely feels like a catch-22.

Thanks,


Benjamin Young






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to