Thanks everybody.

No PVC drain line.

Happy Easter.

Scott

Office: (763) 425-1001 x2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Art Tiroly
Sent: Saturday, March 31, 2018 1:04 PM
To: [email protected]
Subject: RE: PVC drain line

Creating a PVC drain header for the branch lines should not be done.
Same reason as not running PVC with sprinkler head tees. Not an approved 
material.

Art Tiroly
ATCO Fire Protection

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Scott Futrell
Sent: Friday, March 30, 2018 6:24 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: PVC drain line

Yes, I do think that is the way to go, but it is a sprink contractor making the 
suggestion. I'm trying to justify a response one way or the other.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Friday, March 30, 2018 5:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: PVC drain line

I thought I was going to be called crazy for suggesting a valve at the end of 
each line and then running it in PVC.  It would be expensive for sure.  Let me 
know if you are going to go that way and I will be stock in the valve suppliers.

Practically, run it in steel and call it good.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Matthew J Willis
Sent: Friday, March 30, 2018 3:13 PM
To: Forum 
<[email protected]<mailto:[email protected]>>
Subject: RE: PVC drain line

So,
The answer would be no. Right?
Plastic is fine for drain, not listed. But all piping before the valve is.

R/
Matt

Sent from my Verizon 4G LTE Droid
On Mar 30, 2018 4:10 PM, Scott Futrell 
<[email protected]<mailto:[email protected]>> wrote:
I can't see a valve at the end of each line being practical.  Then you'd need a 
lift to drain them when you wanted to use it and these are >25K square foot 
systems, so many valves.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jeff Normand
Sent: Friday, March 30, 2018 5:07 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: PVC drain line

I say it's fine if you have drain valves at the end of each line and transition 
to pvc after the valve. But that may be expensive.

So I say pvc is ok after the drain valve.

But is that practical?

On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell 
<[email protected]<mailto:[email protected]>> wrote:

A Friday afternoon conundrum for the group.



I have a client with corrosion issues in several wet, twenty year old, ESFR, 
warehouse systems.  These are center-fed systems.  Yes, center-fed. So all of 
the branchlines are dead ends.  Corrosion scale and sludge is pushed into the 
ends of the lines.  Flushing will be done.  End of the day though the client 
wants to add a tie-in drain line connecting all the ends of all the lines to 
drain/flush in the future.  It has been suggested that schedule 40 PVC might be 
used for these tie-in drains.



My response so far:



Practically, plastic should be okay.



But, it would not be recognized in NFPA 13.  Also, because it could fail in a 
fire, and we would expect high challenge fires in warehouses filled with 
combustibles like pallets and plastics, if it failed before the sprinklers 
operated, or before they were winning the battle you would have a potential 
system failure.  Chances are probably remote, but they would exist with the 
right (wrong) conditions.



I would expect that a knowledgeable inspector would question the installation 
at least.



I wouldn't specify it, but schedule 40 PVC might be an option for what you are 
trying to accomplish cost-effectively.



What say ye all?



Scott Futrell

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to