As a plan specifier, plan reviewer and an investigator I see designs right to 
the supply and then as-built conditions far worse (read more demanding) than 
the design submitted with the calcs.  This is not a regional observation.

Additionally, I am aware of communities that lower elevated tank levels 20’ in 
winter to lower heating costs.  Contractors in those areas do NOT adjust flow 
tests for this seasonal variation.

No safety margin what-so-ever in NFPA 13 is unreasonable for a design standard.

Arguments on the floor including ‘requiring all systems to have back-up power’ 
were ridiculous.

Scott

Office: (763) 425-1001 x2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, June 15, 2018 2:16 PM
To: [email protected]
Subject: RE: Safety Margin

That was the conversation on the floor of the code hearing.  The concerns 
underscored by the CAM were not about whether safety factor is a good practice, 
it was that a fixed minimum value as high as 10 PSI could trigger all sorts of 
cost-impact consequences, particularly in areas where pressures are middling to 
poor – in Rhode Island, 10 PSI could be 25-30% of the available pressure.

In the West, due primarily to the politics of drought, water districts are 
using models in lieu of physical flow tests.  Prudent and conservative 
programming makes it possible for them to issue safeguarded values from which 
it’s not necessary to reduce the available pressure.  For ex., City of San 
Diego uses a three-level safety factor in their (highly accurate) models:  
starting with legacy drought water levels in the reservoirs, then factor the 
highest seasonal demand, then the highest peak day demand of that season.   The 
values we’re getting are usually significantly lower than what can be measured 
on the hydrant, and this practice isn’t without controversy because there are 
obvious complications that can and do occur, particularly with existing systems 
based on 20-year old (and older) pressures that were physically measured (with 
crappy equipment) when first designed and built.

But if modeling becomes the new normal, prudent water district engineering 
departments and fire departments they serve can coordinate manipulating data to 
include reasonable safety factors.  The range of variation in pressures, 
accuracy of flow test equipment, the use of modeling in many areas … there are 
too many variables to set a fixed minimum safety factor based on PSI, IMHO.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Parsley Consulting
Sent: Friday, June 15, 2018 12:00 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Safety Margin

Richard,

If my memory is accurate of the issues raised in the discussion that ambiguity 
was a part of the differing viewpoints.

Some argued that 10 psi was not workable in their locale as their pressures 
were so limited that an imposition of 10 psi was simply to drastic and would 
result in much larger pipe sizes as a result.

Others argued that 10 psi was not enough, and in their area 10 psi didn't equal 
10%, and there was some reluctance to base their designs on a pressure greater 
than 90% of the available.

It was quite a discussion.
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 06/15/2018 10:23 AM, Richard Carr wrote:
Even though it is not in NFPA most AHJ’s require some sort of safety margin, 
10%, 10 psi which we have had to provide for a long time so most designers know 
to leave safety margin in the calc’s. it would be nice if they all used the 
same amount.

Richard M. Carr, SET
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NC  28731

[email protected]<mailto:[email protected]>
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile

[cid:[email protected]]

[cid:[email protected]]


From: Sprinklerforum 
<[email protected]><mailto:[email protected]>
 On Behalf Of Parsley Consulting
Sent: Friday, June 15, 2018 1:22 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Safety Margin

Scott,

Based on the material which was presented to the -24 and -291 committee 
meetings I believed the proposed safety margin and the means to calculate that 
margin there was some merit in the proposal.

For reasons I don't quite remember the PI was voted down at the 2nd draft 
meeting.  I listened to some of the discussion, and there were some good points 
made.  I'm not terribly surprised it failed at the convention level.  Perhaps 
the attendees were following the lead of the technical committees, and 
declining to overrule their decision.

sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 06/15/2018 8:09 AM, Scott Futrell wrote:

Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 failed, 
so it won't be included or required.



I consider this unfortunate, but I'd guess that not everyone on the forum would 
agree.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



-----Original Message-----

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]<mailto:[email protected]>

Sent: Thursday, June 14, 2018 5:46 PM

To: 
[email protected]<mailto:[email protected]>

Subject: NFPA Vegas Convention



I didn't make it again this year.

"Caputo" is the only speaker name I recognized.

Anybody have any earthshaking epiphanies?





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org






_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to