If I remember correctly, I have seen the automatic fill lines enter near the 
discharge. However, it would pipe up the inside of the tank near the top with a 
turn down and discharge high. This was on large tanks and it has been a few 
years.



Bobby Gillett
Seago Fire Protection, LLC
850-217-3899 cell
850-836-2288 office
850-836-2277 fax


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Kyle.Montgomery <[email protected]>
Sent: Thursday, February 28, 2019 9:42 AM
To: [email protected]
Subject: Suction Tank Question


NFPA 22 states the following:



14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into 
the opposite half of the tanks from the pump suction pipe.



Does that mean that the fill line has to be directly across (opposite) the tank 
from the pump suction? If I’ve got a tank with a diameter of 90 feet, do I 
really need to run the fill line all the way around to the other side or is 
there an acceptable minimum distance? It seems like overkill to require the 
fill line to be 90 feet away from the suction. I mean, if it was a small tank 
with a diameter of 20 feet, then only 20 feet away would be acceptable, right?



Any thoughts?



Kyle Montgomery

 [cid:[email protected]]

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

[email protected]<mailto:[email protected]>




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to