That's the situation we've got. Is that considered acceptable? Technically the pump suction is on the bottom half and the fill is on the top half, so opposite halves, right?
-Kyle M From: Sprinklerforum [mailto:[email protected]] On Behalf Of Bobby Sent: Thursday, February 28, 2019 9:08 AM To: [email protected] Subject: [EXTERNAL] Re: Suction Tank Question If I remember correctly, I have seen the automatic fill lines enter near the discharge. However, it would pipe up the inside of the tank near the top with a turn down and discharge high. This was on large tanks and it has been a few years. Bobby Gillett Seago Fire Protection, LLC 850-217-3899 cell 850-836-2288 office 850-836-2277 fax ________________________________ From: Sprinklerforum <[email protected]<mailto:[email protected]>> on behalf of Kyle.Montgomery <[email protected]<mailto:[email protected]>> Sent: Thursday, February 28, 2019 9:42 AM To: [email protected]<mailto:[email protected]> Subject: Suction Tank Question NFPA 22 states the following: 14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into the opposite half of the tanks from the pump suction pipe. Does that mean that the fill line has to be directly across (opposite) the tank from the pump suction? If I've got a tank with a diameter of 90 feet, do I really need to run the fill line all the way around to the other side or is there an acceptable minimum distance? It seems like overkill to require the fill line to be 90 feet away from the suction. I mean, if it was a small tank with a diameter of 20 feet, then only 20 feet away would be acceptable, right? Any thoughts? Kyle Montgomery [cid:[email protected]] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 [email protected]<mailto:[email protected]>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org