IMHO the intent of the rule is to get the inlet away from the suction so as to 
minimize the potential for air entrainment, as has been discussed. As written 
the inlet needs to be on the opposite half of the tank. This could mean a ½ 
diameter away, or maybe at least 90 degrees along the outside of a round tank 
from the pump suction nozzle.

Could it be located closer to the suction without causing problems – probably, 
especially on a 90 ft. diameter tank, but that is not how the standard is 
written.  Perhaps it may be time for a suggested improvement to be sent to the 
NFPA 22 committee.  Remember also that the fill line for a 90 ft. diameter tank 
is likely going to be much larger than one for a 20 ft. diameter tank, which 
makes a difference as well.

-Mark

Note: None of the above should be interpreted as an official opinion or 
position of the NFPA 22 technical committee.


[Visit our Website at www.SummitCoUS.com]<http://www.SummitCoUS.com>    Mark 
Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Thursday, February 28, 2019 9:42 AM
To: [email protected]
Subject: Suction Tank Question

NFPA 22 states the following:

14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge into 
the opposite half of the tanks from the pump suction pipe.

Does that mean that the fill line has to be directly across (opposite) the tank 
from the pump suction? If I’ve got a tank with a diameter of 90 feet, do I 
really need to run the fill line all the way around to the other side or is 
there an acceptable minimum distance? It seems like overkill to require the 
fill line to be 90 feet away from the suction. I mean, if it was a small tank 
with a diameter of 20 feet, then only 20 feet away would be acceptable, right?

Any thoughts?

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to