Maybe this is a dumb question, but much like the return line for a relief, 
if the fill line is piped below the lowest level of water after system 
demand is satisfied, is there any way air could become entrapped?  Other 
than maybe some splashing?



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   "Mark Sornsin [FAR]" <[email protected]>
To:     "'[email protected]'" 
<[email protected]>
Date:   02/28/2019 03:25 PM
Subject:        RE: Suction Tank Question
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 

IMHO the intent of the rule is to get the inlet away from the suction so 
as to minimize the potential for air entrainment, as has been discussed. 
As written the inlet needs to be on the opposite half of the tank. This 
could mean a ½ diameter away, or maybe at least 90 degrees along the 
outside of a round tank from the pump suction nozzle.
 
Could it be located closer to the suction without causing problems – 
probably, especially on a 90 ft. diameter tank, but that is not how the 
standard is written.  Perhaps it may be time for a suggested improvement 
to be sent to the NFPA 22 committee.  Remember also that the fill line for 
a 90 ft. diameter tank is likely going to be much larger than one for a 20 
ft. diameter tank, which makes a difference as well.
 
-Mark
 
Note: None of the above should be interpreted as an official opinion or 
position of the NFPA 22 technical committee.
 


Mark Sornsin  
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585

From: Sprinklerforum [
mailto:[email protected]] On Behalf Of 
Kyle.Montgomery
Sent: Thursday, February 28, 2019 9:42 AM
To: [email protected]
Subject: Suction Tank Question
 
NFPA 22 states the following:
 
14.4.10.1 Pipes for the automatic filling of suction tanks shall discharge 
into the opposite half of the tanks from the pump suction pipe.
 
Does that mean that the fill line has to be directly across (opposite) the 
tank from the pump suction? If I’ve got a tank with a diameter of 90 feet, 
do I really need to run the fill line all the way around to the other side 
or is there an acceptable minimum distance? It seems like overkill to 
require the fill line to be 90 feet away from the suction. I mean, if it 
was a small tank with a diameter of 20 feet, then only 20 feet away would 
be acceptable, right?
 
Any thoughts?
 
Kyle Montgomery
 
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]
 
 

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=ScOwpnIuDgO9vQxhFnt8NAFUF35YZwhJfHxFW7l5qMc&s=6mtEAnUdIJNpwSWVvLVsznuORSZW4baIahOW7knDNms&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to