ESFR is not the end all, be all of storage protection.  It is not
appropriate for a building like that.  In that case, you need to find an SSU
/ in-rack system or other storage sprinkler that will work.  But, ESFR is a
no go.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <[email protected]> On
Behalf Of Cliff Whitfield
Sent: Monday, April 1, 2019 8:54 AM
To: [email protected]
Subject: RE: ESFR and Baffles

 

What do you do when you have ESFR in a structure with W-Beams that are less
than 8' apart but too deep to get the proper deflector distance beneath
them?

 

Cliff Whitfield, SET

President

 

Fire Design, Inc.

184 Comfort Place

Burnsville, NC 28714

Ph: 828-284-4772

 



 

 <mailto:[email protected]> [email protected]

 <http://www.fire-design.com/> www.fire-design.com

 

From: Sprinklerforum <[email protected]> On
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, April 1, 2019 11:22 AM
To: [email protected]
Subject: ESFR and Baffles

 

Posting to help a friend. 

 

I've always been taught that ESFR is 8' minimum. You are not permitted to
use baffles or anything to reduce the minimum distance between ESFR
sprinklers. There is a respected FPE challenging this statement and trying
to use baffles to allow ESFR to be less than 8'.  My friend asked my
opinion, but I wanted to see if others had any thoughts on this. 

 

 

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

 <http://www.mfpdesign.com> www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=link> www.avast.com 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to