My take on that is it has to do with heat flow.  Top cords / joists / etc. with 
a depth greater than 4” interfere too much with heat flow.  No obstruction to 
water distribution, but a delay in activation.

 

Ed K

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Monday, April 01, 2019 1:01 PM
To: [email protected]
Subject: RE: [EXTERNAL] RE: ESFR and Baffles

 

So, here’s a related question I’ve been pondering: What if you have Wood Joist 
Construction (technically combustible obstructed, right?) but the depth of the 
wood members is relatively short (like 2x6s or something)… are you prohibited 
from using ESFR heads? 

 

It seems strange that you wouldn’t be able to use them in that case, since you 
would be able to maintain the appropriate deflector distance (up to 18” from 
deck is allowable for some ESFRs) and there would be no actual obstruction to 
the sprinklers. Is there something that I am missing?

 

Kyle Montgomery

 

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

[email protected] <mailto:[email protected]> 

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, April 1, 2019 10:14 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: [EXTERNAL] RE: ESFR and Baffles

 

Yes.  There are things you can do to change the building to make it ESFR 
compatible.  But as it was described, you have a building that is not compliant 
with ESFR.

 

Too many people jump to ESFR as the panacea of storage.

 

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=qPqzkIcYhJ2zI_RVIutELOG-iYAapNlejxRnE0NPE0M&e=>
 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com <http://www.mfpdesign.com> 

 

Send large files to us via: https://www.hightail.com/u/MFPDesign 

LinkedIn: https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Steve 
Leyton
Sent: Monday, April 1, 2019 10:11 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: ESFR and Baffles

 

Corollary to The Perfect Answer:    I would say that someone needs to install a 
suspended ceiling to create a conforming application for ESFR.  

 

Steve Leyton

Almost Perfect

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Monday, April 01, 2019 9:51 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: Re: ESFR and Baffles

 

Perfect answer

 

Roland

 





Roland Huggins, PE


Senior Vice President, Engineering & Technical Services


American Fire Sprinkler Association


p:

214-349-5965 ext121


w:

 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__firesprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=Vy-IyFyG1i1tqIk694e9FNZyITZgo96XXvsp9L-xDbE&e=>
 firesprinkler.org  


 
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_firesprinkler.org_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=i2frm7_BmtNa39q2fOGfAK84y6YSKMDhnAiGYrG7hj0&e=>
    
<https://urldefense.proofpoint.com/v2/url?u=https-3A__twitter.com_afsa_status_1039528345367732224&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=qudp3qi8nTBMzUTNEfGjN3rYU8TEoyGg6qG11Kj3PG8&e=>
    
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_company_american-2Dfire-2Dsprinkler-2Dassociation-2Dafsa-2D_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=fkwQKY7bLXMxE2Rz55JW0_e6_uKimObeFz_yX0HV47M&e=>
    
<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.instagram.com_firesprinklerorg_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=k2MBYdoRIHA4uvwl6mWR_cQDUOKyc042SymYX5vDH0c&s=iJzwLIeJSvq69qRqyC7TcbWp3IlEWvJnXtOh4eD-GMI&e=>
 

 

 

On Apr 1, 2019, at 8:56 AM, Shawn Foor <[email protected] 
<mailto:[email protected]> > wrote:

 

I would say you are in a building that you can’t use ESFR heads

 

On Mon, Apr 1, 2019 at 10:53 Cliff Whitfield <[email protected] 
<mailto:[email protected]> > wrote:

What do you do when you have ESFR in a structure with W-Beams that are less 
than 8’ apart but too deep to get the proper deflector distance beneath them?

 

Cliff Whitfield, SET