Yes.  There are things you can do to change the building to make it ESFR 
compatible.  But as it was described, you have a building that is not compliant 
with ESFR.

 

Too many people jump to ESFR as the panacea of storage.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Steve Leyton
Sent: Monday, April 1, 2019 10:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR and Baffles

 

Corollary to The Perfect Answer:    I would say that someone needs to install a 
suspended ceiling to create a conforming application for ESFR.  

 

Steve Leyton

Almost Perfect

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Monday, April 01, 2019 9:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR and Baffles

 

Perfect answer

 

Roland

 





Roland Huggins, PE


Senior Vice President, Engineering & Technical Services


American Fire Sprinkler Association


p:

214-349-5965 ext121


w:

 <http://firesprinkler.org> firesprinkler.org  


 <https://www.facebook.com/firesprinkler.org/>    
<https://twitter.com/afsa/status/1039528345367732224>    
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>   
 <https://www.instagram.com/firesprinklerorg/> 

 

 

On Apr 1, 2019, at 8:56 AM, Shawn Foor <shawn.f...@gmail.com 
<mailto:shawn.f...@gmail.com> > wrote:

 

I would say you are in a building that you can’t use ESFR heads

 

On Mon, Apr 1, 2019 at 10:53 Cliff Whitfield <cl...@fire-design.com 
<mailto:cl...@fire-design.com> > wrote:

What do you do when you have ESFR in a structure with W-Beams that are less 
than 8’ apart but too deep to get the proper deflector distance beneath them?

 

Cliff Whitfield, SET

President

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to