It's been forever since I bid one but would you start a Lowes Garden Center
and work your way down?  

 


Nick Maneen, SET 

c 704.791.7789

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, December 17, 2019 11:51 AM
To: [email protected]
Cc: Steve Leyton
Subject: Hazard Group?

 

We're working on a maintenance warehouse for a community college, set on a
very large campus with lots of landscape.  They are combining landscape and
maintenance departments, so supplies range from grounds-keeping to whatever
they need in the built environment, from fertilizers and athletic field
marking paints to asphaltic coatings to sanitizers and clarifiers for
landscape (higher volumes of pool chems for aquatics center not to be stored
here), adhesives, solvents, lubricants, and low grade stuff like
construction materials and hardware.  There will also be 5 gallon latex
paint buckets ("a few"), and 7-10 containers of gasoline and pre-mixed fuels
not exceeding 35 gallons total.   Only fertilizers and seed are in larger
quantities, bagged on pallets with a pallet here and a pallet there,
otherwise products are in consumer-sized packaging.    Commodities will only
be present in exempt amounts and while a few are highly reactive, except for
fuels and solvents none are flammable liquids.   

 

Individually, there's not any one compelling hazard that defines the storage
but taken together we have some kinda' fire load and would value opinions on
what kinda' fire load that is.   I'm leaning toward EH2 because .  well,
because I'm lazy.   Water pressure's okay, building isn't that very big
(less than 8,000 sq. ft.) and max roof height is 17'.   We're assuming rack
storage (since they aren't going to have a fixture plan before we have to
submit) and a max height of 15'.    If anyone's got the time to throw a dart
at this equation, I'd appreciate the input.  

 

 



 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org