Area/density protection for 15' of rack storage in a 17' building for cartoned 
non-expanded plastic is only .6/2000 (If I am reading the figures correctly).

If the water supply could handle it without a pump, a .6/2000 + EH2 system 
would let them do pretty much whatever they want in the building. For an 8000sf 
facility, if the budget works, they are only talking about a couple thousand 
dollars difference no matter which way they go.

Matt


From: Sprinklerforum <[email protected]> On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Tuesday, December 17, 2019 11:53 AM
To: Prahl, Craig/GVL <[email protected]>; 
[email protected]
Cc: Steve Leyton <[email protected]>
Subject: RE: Hazard Group?

This is more or less the same program that's running in my head right now.   
The pallet loads are mostly large bags of landscape-related materials sitting 
on pallets (for convenience) on the floor and not conventional 4-5' high pallet 
loads.   I'm with you on the rest of the stuff; the asphaltic coatings are in 1 
and 5 gallon containers and there's not that much of this class.  Flammable 
liquids very limited, combustibles all Class 3 from what I can see.    I'm 
comfy with EH2 but I'm pushing them to stay at/under 12'.

Steve

From: Prahl, Craig/GVL [mailto:[email protected]]
Sent: Tuesday, December 17, 2019 9:33 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton
Subject: RE: Hazard Group?

Can you persuade them to configure the storage arrangement and height so that 
it qualifies as Miscellaneous Storage (<12ft)?  With a roof height of only 17 
ft (which I'm not sure if that's at peak or at eave), allowing clearance for 
structure and lights, you might not get a top rack level at 15 ft.  More likely 
if palleted loads are used, you might not even get a 12 ft top rack level in 
that building.

You might have a whole host of flammable and combustible liquids in that list 
besides the fuels and solvents.   Those suspected materials would be asphaltic 
coatings, sanitizers, adhesives, solvents, lubricants.  Looks like mostly Class 
II and III materials.  Some solvents can be Class IB like alcohols and acetone.

Asphaltic materials, and potentially adhesives and lubricants are often 
hydrocarbon based and don't respond to any great degree to water alone once 
ignited.  So depending on the quantities of these materials, it might be 
beneficial to have those items stored in a UL listed Fire Cabinet along with 
the gasoline and mixed fuels.  Get those items out of the general inventory and 
secured separately from the general commodities. I would then be looking at 
General Storage criteria out of NFPA 13 to see if EH2 might be adequate enough 
for the rest of the building.


Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, December 17, 2019 11:51 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Hazard Group?

We're working on a maintenance warehouse for a community college, set on a very 
large campus with lots of landscape.  They are combining landscape and 
maintenance departments, so supplies range from grounds-keeping to whatever 
they need in the built environment, from fertilizers and athletic field marking 
paints to asphaltic coatings to sanitizers and clarifiers for landscape (higher 
volumes of pool chems for aquatics center not to be stored here), adhesives, 
solvents, lubricants, and low grade stuff like construction materials and 
hardware.  There will also be 5 gallon latex paint buckets ("a few"), and 7-10 
containers of gasoline and pre-mixed fuels not exceeding 35 gallons total.   
Only fertilizers and seed are in larger quantities, bagged on pallets with a 
pallet here and a pallet there, otherwise products are in consumer-sized 
packaging.    Commodities will only be present in exempt amounts and while a 
few are highly reactive, except for fuels and solvents none are flammable 
liquids.

Individually, there's not any one compelling hazard that defines the storage 
but taken together we have some kinda' fire load and would value opinions on 
what kinda' fire load that is.   I'm leaning toward EH2 because ...  well, 
because I'm lazy.   Water pressure's okay, building isn't that very big (less 
than 8,000 sq. ft.) and max roof height is 17'.   We're assuming rack storage 
(since they aren't going to have a fixture plan before we have to submit) and a 
max height of 15'.    If anyone's got the time to throw a dart at this 
equation, I'd appreciate the input.


[cid:[email protected]]



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to