I'm presuming the gas in appropriate containers in an appropriate cabinet,
although at the school where I worked the maintenance guys would leave the
gas cans outside or on top of the cabinets.


Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)


On Tue, Dec 17, 2019 at 9:01 AM Steve Leyton via Sprinklerforum <
[email protected]> wrote:

> That’s about right in terms of the mix, but with measurably lower
> quantities.
>
>
>
> SL
>
>
>
> *From:* Nick Maneen [mailto:[email protected]]
> *Sent:* Tuesday, December 17, 2019 8:57 AM
> *To:* [email protected]
> *Cc:* Steve Leyton
> *Subject:* RE: Hazard Group?
>
>
>
> It’s been forever since I bid one but would you start a Lowes Garden
> Center and work your way down?
>
>
>
> *Nick Maneen, SET *
>
> *c* 704.791.7789
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Steve
> Leyton via Sprinklerforum
> *Sent:* Tuesday, December 17, 2019 11:51 AM
> *To:* [email protected]
> *Cc:* Steve Leyton
> *Subject:* Hazard Group?
>
>
>
> We’re working on a maintenance warehouse for a community college, set on a
> very large campus with lots of landscape.  They are combining landscape and
> maintenance departments, so supplies range from grounds-keeping to whatever
> they need in the built environment, from fertilizers and athletic field
> marking paints to asphaltic coatings to sanitizers and clarifiers for
> landscape (higher volumes of pool chems for aquatics center not to be
> stored here), adhesives, solvents, lubricants, and low grade stuff like
> construction materials and hardware.  There will also be 5 gallon latex
> paint buckets (“a few”), and 7-10 containers of gasoline and pre-mixed
> fuels not exceeding 35 gallons total.   Only fertilizers and seed are in
> larger quantities, bagged on pallets with a pallet here and a pallet there,
> otherwise products are in consumer-sized packaging.    Commodities will
> only be present in exempt amounts and while a few are highly reactive,
> except for fuels and solvents none are flammable liquids.
>
>
>
> Individually, there’s not any one compelling hazard that defines the
> storage but taken together we have some kinda’ fire load and would value
> opinions on what kinda’ fire load that is.   I’m leaning toward EH2 because
> …  well, because I’m lazy.   Water pressure’s okay, building isn’t that
> very big (less than 8,000 sq. ft.) and max roof height is 17’.   We’re
> assuming rack storage (since they aren’t going to have a fixture plan
> before we have to submit) and a max height of 15’.    If anyone’s got the
> time to throw a dart at this equation, I’d appreciate the input.
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to