That's about right in terms of the mix, but with measurably lower quantities.

SL

From: Nick Maneen [mailto:[email protected]]
Sent: Tuesday, December 17, 2019 8:57 AM
To: [email protected]
Cc: Steve Leyton
Subject: RE: Hazard Group?

It's been forever since I bid one but would you start a Lowes Garden Center and 
work your way down?

Nick Maneen, SET
c 704.791.7789

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, December 17, 2019 11:51 AM
To: [email protected]
Cc: Steve Leyton
Subject: Hazard Group?

We're working on a maintenance warehouse for a community college, set on a very 
large campus with lots of landscape.  They are combining landscape and 
maintenance departments, so supplies range from grounds-keeping to whatever 
they need in the built environment, from fertilizers and athletic field marking 
paints to asphaltic coatings to sanitizers and clarifiers for landscape (higher 
volumes of pool chems for aquatics center not to be stored here), adhesives, 
solvents, lubricants, and low grade stuff like construction materials and 
hardware.  There will also be 5 gallon latex paint buckets ("a few"), and 7-10 
containers of gasoline and pre-mixed fuels not exceeding 35 gallons total.   
Only fertilizers and seed are in larger quantities, bagged on pallets with a 
pallet here and a pallet there, otherwise products are in consumer-sized 
packaging.    Commodities will only be present in exempt amounts and while a 
few are highly reactive, except for fuels and solvents none are flammable 
liquids.

Individually, there's not any one compelling hazard that defines the storage 
but taken together we have some kinda' fire load and would value opinions on 
what kinda' fire load that is.   I'm leaning toward EH2 because ...  well, 
because I'm lazy.   Water pressure's okay, building isn't that very big (less 
than 8,000 sq. ft.) and max roof height is 17'.   We're assuming rack storage 
(since they aren't going to have a fixture plan before we have to submit) and a 
max height of 15'.    If anyone's got the time to throw a dart at this 
equation, I'd appreciate the input.


[cid:[email protected]]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to