Thanks Guys.
I do understand we are responsible to inspect the installed system as is. 
However, if it is not in conformance with current Code requirements, I would 
like to give the Owner the option to update it.

Ken Haney
Certified Engineering Tech
Haney Fire Protection, Inc.
610.217.0347
[email protected]

From: tstone52--- via Sprinklerforum
Sent: Thursday, June 11, 2020 1:44 PM
To: [email protected]
Cc: [email protected]
Subject: RE: Unsprinklered Parking Garage

To my knowledge that is not an inspection item per NFPA 25. You can ask the 
owner after you have performed an NFPA 25 Inspection.

Regards,
G. Tim Stone
 
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
 
   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]

From: Sprinklerforum <[email protected]> On Behalf 
Of Ken Haney via Sprinklerforum
Sent: Thursday, June 11, 2020 1:24 PM
To: [email protected]
Cc: Ken Haney <[email protected]>
Subject: Unsprinklered Parking Garage

Hello All,
I am a first time participant, so please bear with me. We have a new inspection 
customer in the State of NJ that has a fully sprinklered (6) story office 
building with a standpipe in the stair tower.  It sits on an underground 
parking garage that has no standpipe or sprinkler protection. Does anyone know 
if sprinklers and/or a standpipe are a Code requirement for this situation?
Thanks,

Ken Haney
Certified Engineering Tech
Haney Fire Protection, Inc.
610.217.0347
[email protected]