Hope everyone is healthy.

Remember that including the recommendation to sprinkler the garage in your NFPA 
25 report you are outside the parameters of the requirements of NFPA 25 and can 
possible expose your company to un-expected risks. Place all recommendations 
not covered in NFPA 25 for improvements/extend protection of sprinkler system 
in a document separate from your NFPA 25 inspection report.

Have a fire safe day!

Jim Davidson

From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Thursday, June 11, 2020 2:26 PM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; [email protected]; Ken Haney 
<[email protected]>
Subject: RE: [EXTERNAL] RE: Unsprinklered Parking Garage

Was the system code compliant when installed and the certificate of occupancy 
issued?  If it was, it doesn’t matter if it meets current code unless there 
were building changes that according to code required areas or systems to be 
updated.

Most owners are not going to update fire protection systems unless the law 
requires them to do so.  It’s a huge expenditure with little to no return on 
investment for property owners.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Ken Haney via Sprinklerforum
Sent: Thursday, June 11, 2020 2:07 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Ken Haney <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: Unsprinklered Parking Garage

Thanks Guys.
I do understand we are responsible to inspect the installed system as is. 
However, if it is not in conformance with current Code requirements, I would 
like to give the Owner the option to update it.

Ken Haney
Certified Engineering Tech
Haney Fire Protection, Inc.
610.217.0347
[email protected]<mailto:[email protected]>

From: tstone52--- via 
Sprinklerforum<mailto:[email protected]>
Sent: Thursday, June 11, 2020 1:44 PM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: RE: Unsprinklered Parking Garage

To my knowledge that is not an inspection item per NFPA 25. You can ask the 
owner after you have performed an NFPA 25 Inspection.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]<mailto:[email protected]>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Ken Haney via Sprinklerforum
Sent: Thursday, June 11, 2020 1:24 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Ken Haney <[email protected]<mailto:[email protected]>>
Subject: Unsprinklered Parking Garage

Hello All,
I am a first time participant, so please bear with me. We have a new inspection 
customer in the State of NJ that has a fully sprinklered (6) story office 
building with a standpipe in the stair tower.  It sits on an underground 
parking garage that has no standpipe or sprinkler protection. Does anyone know 
if sprinklers and/or a standpipe are a Code requirement for this situation?
Thanks,

Ken Haney
Certified Engineering Tech
Haney Fire Protection, Inc.
610.217.0347
[email protected]<mailto:[email protected]>



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to