My understanding had always been this was mainly related to shelves and the 
like as an obstruction since the head is going to basically inundate the 
closet.  I believe it was Mr. Huggins that once reminded us that water isn't 
like light and you don't have to see the head to get wet, as was a popular 
method of evaluating obstructions on the enforcement side at the time.  FWIW 
9.5.6.6.1 is worth a look as it could apply to most closets I can think of as 
long as the head location was right.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 11:36 AM
To: [email protected]
Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]>
Subject: Closets and Clearance from Deflector to Storage

 
BE ADVISED - This email originated outside EMCOR. 
 

NFPA 13 (2019 edition) states the following in two sections:

https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  Closets. In all closets and compartments, including those closets housing 
mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a 
single sprinkler at the highest ceiling level shall be sufficient without 
regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 
https://urldefense.com/v3/__http://9.5.6.2__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWK_S5DY$
 , 
https://urldefense.com/v3/__http://9.5.6.3__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUaCDv_qW$
 , 
https://urldefense.com/v3/__http://9.5.6.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUWJSGby8$
 , or 
https://urldefense.com/v3/__http://9.5.6.5__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUYi1bnkN$
  are met, the clearance between the deflector and the top of storage or 
contents of the room shall be 18 in. (450 mm) or greater.

Section 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  states "....a single sprinkler at the highest ceiling level shall be 
sufficient without regard to obstructions or minimum distance to the wall."  
Does 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  allow a sprinkler to be less than 18 inches from the storage in a closet?  
Section 
https://urldefense.com/v3/__http://9.5.6.1__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQURUORag8$
  does not specifically say that 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  is an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered an 
"obstruction", then it would seem that 
https://urldefense.com/v3/__http://9.5.5.4__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUf8clHlv$
  would allow storage that is less than 18 inches from the sprinkler deflector 
in a closet.

Thanks in advance.

Pete
Dept of VA

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PJVUyG8T3MKXlZlgRRf0dwy7i4YdVrTtqX072L0iAQnzaA2NLRb1EVeQUePq5JbQ$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to