Thanks for that clarification. I missed that. Pete
-----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Dane Long via Sprinklerforum Sent: Thursday, July 1, 2021 12:51 PM To: [email protected] Cc: Dane Long <[email protected]>; Larrimer, Peter A (HEFP\19HEF) <[email protected]> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. Your minimum discharge is going to automatically be the 7psi, so you're going to be flooding the closet anyway. Thanks, Dane Long, AET Engineering Technician | Bamford Fire Sprinkler Co., Inc. P: 785.825.7710 F: 785.825.0667 A: 1383 W. North Street Salina, KS 67401 -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To: [email protected] Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]> Subject: Closets and Clearance from Deflector to Storage NFPA 13 (2019 edition) states the following in two sections: 9.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall. 9.5.6 Clearance from Deflector to Storage. 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or 9.5.6.5 are met, the clearance between the deflector and the top of storage or contents of the room shall be 18 in. (450 mm) or greater. Section 9.5.5.4 states "....a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the storage in a closet? Section 9.5.6.1 does not specifically say that 9.5.5.4 is an exception to the 18 inch storage clearance requirement. However, if the storage less than 18 inches from the deflector is considered an "obstruction", then it would seem that 9.5.5.4 would allow storage that is less than 18 inches from the sprinkler deflector in a closet. Thanks in advance. Pete Dept of VA _______________________________________________ Sprinklerforum mailing list [email protected] https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 _______________________________________________ Sprinklerforum mailing list [email protected] https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org