Thanks for that clarification.  I missed that.

Pete

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Dane Long via Sprinklerforum
Sent: Thursday, July 1, 2021 12:51 PM
To: [email protected]
Cc: Dane Long <[email protected]>; Larrimer, Peter A (HEFP\19HEF) 
<[email protected]>
Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

Peter,

One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
you have mechanical equipment like a furnace, you're not really going to have 
much room to store anything in this closet. An example would be a closet with 
an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
Your minimum discharge is going to automatically be the 7psi, so you're going 
to be flooding the closet anyway.

Thanks,






Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Sent: Thursday, July 1, 2021 10:36 AM
To: [email protected]
Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]>
Subject: Closets and Clearance from Deflector to Storage

NFPA 13 (2019 edition) states the following in two sections:

9.5.5.4 Closets. In all closets and compartments, including those closets 
housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, 
a single sprinkler at the highest ceiling level shall be sufficient without 
regard to obstructions or minimum distance to the wall.
9.5.6 Clearance from Deflector to Storage.
9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
9.5.6.5 are met, the clearance between the deflector and the top of storage or 
contents of the room shall be 18 in. (450 mm) or greater.

Section 9.5.5.4 states "....a single sprinkler at the highest ceiling level 
shall be sufficient without regard to obstructions or minimum distance to the 
wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from the 
storage in a closet?  Section 9.5.6.1 does not specifically say that
9.5.5.4 is an exception to the 18 inch storage clearance requirement.

However, if the storage less than 18 inches from the deflector is considered an 
"obstruction", then it would seem that 9.5.5.4 would allow storage that is less 
than 18 inches from the sprinkler deflector in a closet.

Thanks in advance.

Pete
Dept of VA

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;reserved=0

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to