The committee discussion on this change was the in a 400 cubic foot enclosure, it doesn’t matter where the sprinkler is relative to the shelf. Think about in rack sprinklers and the product loads…. I agree there should be concern for bumping the sprinkler but no one is loading the closet with a forklift so….
Bob Caputo - Sent from my iPhone > On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum > <[email protected]> wrote: > > From an old fire guys perspective I’d be more concerned with accidental head > breakage than water dispersal. > > Best. > > >> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum >> <[email protected]> wrote: >> >> >> Thanks for that clarification. I missed that. >> >> Pete >> >> -----Original Message----- >> From: Sprinklerforum <[email protected]> On >> Behalf Of Dane Long via Sprinklerforum >> Sent: Thursday, July 1, 2021 12:51 PM >> To: [email protected] >> Cc: Dane Long <[email protected]>; Larrimer, Peter A (HEFP\19HEF) >> <[email protected]> >> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage >> >> Peter, >> >> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if >> you have mechanical equipment like a furnace, you're not really going to >> have much room to store anything in this closet. An example would be a >> closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3. >> Your minimum discharge is going to automatically be the 7psi, so you're >> going to be flooding the closet anyway. >> >> Thanks, >> >> >> >> >> >> >> Dane Long, AET >> Engineering Technician | Bamford Fire Sprinkler Co., Inc. >> P: 785.825.7710 >> F: 785.825.0667 >> A: 1383 W. North Street Salina, KS 67401 >> >> >> >> -----Original Message----- >> From: Sprinklerforum <[email protected]> On >> Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum >> Sent: Thursday, July 1, 2021 10:36 AM >> To: [email protected] >> Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]> >> Subject: Closets and Clearance from Deflector to Storage >> >> NFPA 13 (2019 edition) states the following in two sections: >> >> 9.5.5.4 Closets. In all closets and compartments, including those closets >> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in >> size, a single sprinkler at the highest ceiling level shall be sufficient >> without regard to obstructions or minimum distance to the wall. >> 9.5.6 Clearance from Deflector to Storage. >> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or >> 9.5.6.5 are met, the clearance between the deflector and the top of storage >> or contents of the room shall be 18 in. (450 mm) or greater. >> >> Section 9.5.5.4 states "....a single sprinkler at the highest ceiling level >> shall be sufficient without regard to obstructions or minimum distance to >> the wall." Does 9.5.5.4 allow a sprinkler to be less than 18 inches from >> the storage in a closet? Section 9.5.6.1 does not specifically say that >> 9.5.5.4 is an exception to the 18 inch storage clearance requirement. >> >> However, if the storage less than 18 inches from the deflector is considered >> an "obstruction", then it would seem that 9.5.5.4 would allow storage that >> is less than 18 inches from the sprinkler deflector in a closet. >> >> Thanks in advance. >> >> Pete >> Dept of VA >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&reserved=0 >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org