The committee discussion on this change was the in a 400 cubic foot enclosure, 
it doesn’t matter where the sprinkler is relative to the shelf.  Think about in 
rack sprinklers and the product loads…. I agree there should be concern for 
bumping the sprinkler but no one is loading the closet with a forklift so…. 

Bob Caputo - Sent from my iPhone


> On Jul 1, 2021, at 2:52 PM, BRUCE VERHEI via Sprinklerforum 
> <[email protected]> wrote:
> 
> From an old fire guys perspective I’d be more concerned with accidental head 
> breakage than water dispersal.
> 
> Best.
> 
> 
>> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum 
>> <[email protected]> wrote:
>> 
>> 
>> Thanks for that clarification.  I missed that.
>> 
>> Pete
>> 
>> -----Original Message-----
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Dane Long via Sprinklerforum
>> Sent: Thursday, July 1, 2021 12:51 PM
>> To: [email protected]
>> Cc: Dane Long <[email protected]>; Larrimer, Peter A (HEFP\19HEF) 
>> <[email protected]>
>> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage
>> 
>> Peter,
>> 
>> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
>> you have mechanical equipment like a furnace, you're not really going to 
>> have much room to store anything in this closet. An example would be a 
>> closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
>> Your minimum discharge is going to automatically be the 7psi, so you're 
>> going to be flooding the closet anyway.
>> 
>> Thanks,
>> 
>> 
>> 
>> 
>> 
>> 
>> Dane Long, AET
>> Engineering Technician | Bamford Fire Sprinkler Co., Inc.
>> P:    785.825.7710
>> F:    785.825.0667
>> A:   1383 W. North Street  Salina, KS  67401
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
>> Sent: Thursday, July 1, 2021 10:36 AM
>> To: [email protected]
>> Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]>
>> Subject: Closets and Clearance from Deflector to Storage
>> 
>> NFPA 13 (2019 edition) states the following in two sections:
>> 
>> 9.5.5.4 Closets. In all closets and compartments, including those closets 
>> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in 
>> size, a single sprinkler at the highest ceiling level shall be sufficient 
>> without regard to obstructions or minimum distance to the wall.
>> 9.5.6 Clearance from Deflector to Storage.
>> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
>> 9.5.6.5 are met, the clearance between the deflector and the top of storage 
>> or contents of the room shall be 18 in. (450 mm) or greater.
>> 
>> Section 9.5.5.4 states "....a single sprinkler at the highest ceiling level 
>> shall be sufficient without regard to obstructions or minimum distance to 
>> the wall."  Does 9.5.5.4 allow a sprinkler to be less than 18 inches from 
>> the storage in a closet?  Section 9.5.6.1 does not specifically say that
>> 9.5.5.4 is an exception to the 18 inch storage clearance requirement.
>> 
>> However, if the storage less than 18 inches from the deflector is considered 
>> an "obstruction", then it would seem that 9.5.5.4 would allow storage that 
>> is less than 18 inches from the sprinkler deflector in a closet.
>> 
>> Thanks in advance.
>> 
>> Pete
>> Dept of VA
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;reserved=0
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;reserved=0
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to