That is a great reason why you want to get your system water tight asap. When a 
soaked worker comes out of the closet with a soldering torch and a story about 
a sprinkler that "went off for no reason" - you will have a heads up before you 
spend hours trying to find an open outlet. 

Matt 


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of BRUCE VERHEI via Sprinklerforum
Sent: Thursday, July 01, 2021 2:52 PM
To: [email protected]
Cc: BRUCE VERHEI <[email protected]>; Dane Long <[email protected]>; 
Larrimer, Peter A (HEFP\19HEF) <[email protected]>
Subject: RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

From an old fire guys perspective I’d be more concerned with accidental head 
breakage than water dispersal.

Best.


> On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum 
> <[email protected]> wrote:
> 
>  
> Thanks for that clarification.  I missed that.
> 
> Pete
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Dane Long via Sprinklerforum
> Sent: Thursday, July 1, 2021 12:51 PM
> To: [email protected]
> Cc: Dane Long <[email protected]>; Larrimer, Peter A (HEFP\19HEF) 
> <[email protected]>
> Subject: [EXTERNAL] RE: Closets and Clearance from Deflector to 
> Storage
> 
> Peter,
> 
> One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if 
> you have mechanical equipment like a furnace, you're not really going to have 
> much room to store anything in this closet. An example would be a closet with 
> an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or 392ft3.
> Your minimum discharge is going to automatically be the 7psi, so you're going 
> to be flooding the closet anyway.
> 
> Thanks,
> 
> 
> 
> 
> 
> 
> Dane Long, AET
> Engineering Technician | Bamford Fire Sprinkler Co., Inc.
> P:    785.825.7710
> F:    785.825.0667
> A:   1383 W. North Street  Salina, KS  67401
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
> Sent: Thursday, July 1, 2021 10:36 AM
> To: [email protected]
> Cc: Larrimer, Peter A (HEFP\19HEF) <[email protected]>
> Subject: Closets and Clearance from Deflector to Storage
> 
> NFPA 13 (2019 edition) states the following in two sections:
> 
> 9.5.5.4 Closets. In all closets and compartments, including those closets 
> housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in 
> size, a single sprinkler at the highest ceiling level shall be sufficient 
> without regard to obstructions or minimum distance to the wall.
> 9.5.6 Clearance from Deflector to Storage.
> 9.5.6.1* Unless the requirements of 9.5.6.2, 9.5.6.3, 9.5.6.4, or
> 9.5.6.5 are met, the clearance between the deflector and the top of storage 
> or contents of the room shall be 18 in. (450 mm) or greater.
> 
> Section 9.5.5.4 states "....a single sprinkler at the highest ceiling 
> level shall be sufficient without regard to obstructions or minimum 
> distance to the wall."  Does 9.5.5.4 allow a sprinkler to be less than 
> 18 inches from the storage in a closet?  Section 9.5.6.1 does not 
> specifically say that
> 9.5.5.4 is an exception to the 18 inch storage clearance requirement.
> 
> However, if the storage less than 18 inches from the deflector is considered 
> an "obstruction", then it would seem that 9.5.5.4 would allow storage that is 
> less than 18 inches from the sprinkler deflector in a closet.
> 
> Thanks in advance.
> 
> Pete
> Dept of VA
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;res
> erved=0
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://gcc02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists
> .firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&a
> mp;data=04%7C01%7C%7C171fd521855d42ea5bbf08d93cb07d43%7Ce95f1b23abaf45
> ee821db7ab251ab3bf%7C0%7C0%7C637607551271236540%7CUnknown%7CTWFpbGZsb3
> d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7
> C3000&amp;sdata=W3YDQ67bNbkjs1e471XyWxEEvY5bleyBqDOI5FjJ9ak%3D&amp;res
> erved=0 _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,erCvG8NFI
> RKPx1FGM-u52cSaMbeXKr9pA3uPTzUI4t4G_zQAMSbpr3W89ckLiPP_P8EB8MBMy0n4uHR
> ge6Hr0Rk08y8YKrCH5sVZ4OSB2VBIP0_LlGWMb-ECH-s,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,Rtaz7xhDjw7hznfEHDCyEIB8st_oAylFqgd3uN6v9qEImsjHMzfR5Se0Rww1NP4hvJpOAK1_X52Ut4ItoI6SH_usAXNVdASupU5hSXs0KxlaKgfkttZjcUPxh9I,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to