Good morning Campers.  Looking for advice and comments.

I have an existing diesel driven fire pump in a prefabricated pump house
installed in 2012 serving 2 apartment buildings.

I first tested this pump in 2017, had 13 hours on it, ran fine but we ran
out of water at just about 100% capacity.

Spent the day with the water department a few days later checking
underground valves, flowing a few street main’s hydrants, basically came to
the conclusion that this is all we got.  Wrote up a report, suggested they
hire an FPE to see if the pump’s tested capacity meets requirements, how did
this happen, what about the hydrants off this system, stuff like that.  I
think I stirred the sleepy caldron a little.

Didn’t hear back from the client until this spring.  Apparently they changed
ITM contractors and the new one didn’t pan out.  They had a balcony fire May
2021, gas grille, 13R system with no attic protection, non-completed attic
separations and fire walls, etc.  Fortunately they had a response so quickly
it never made it to penetrate the eaves and soffits and was extinguished
between the 5th and 6th (top) floors.  Local FD must have had a field day
with a Q20 of about 800 and closest city hydrant ¼ mile away.  Waiting for
incident report to review.

 

So back to my query.  It’s a xy&em pump house.  All welded sch40 and
painted.  Not the greatest build as there’s a 6” BFP vertically installed
right off the incoming service with elbows turning it around and down to the
floor to feed the pump.  Just a few spacers in the piping so no room for
slipping in this device unless something gets removed or moved.  4-15 of #20
(2013) says between the pump discharge and check and I get that but also
defers to the mfgr. for direction.  Looking at the various offerings most
are a little vague on placement and even one says after the pump discharge
valve.  Without major surgery, I have 2 spots to slip in this 20” long
device.  I can remove the relief valve between the discharge increaser and
pump check and put it there ‘or’ I can remove the tee feeding a 6” storz and
check located between the discharge valve and the city bypass.  The former
will allow me to test through the device but the latter will not.  I don’t
believe either of these appurtenances are necessary and I will explain (he’s
still rambling?  Jeepers….).  The engine is a small JD inline 4 running 3000
rpm, single ECM, max. speed is 3300.  Churn is 155 at 3025.  I haven’t
physically done it but if I extrapolate to 3300 I get 170 psi.  I’m below
175 so I think the PRV can go.  If I opt to remove the storz I can but
testing this pump will have to be via the 3 hydrants it serves, in addition
to the 2 buildings.  I honestly don’t know why the engineer (small E) had a
storz included as this house it atop a hill in the woods ½ mile away from a
city hydrant and these buildings.

 

OK, done rambling.  Loose the PRV or keep scratching my head?

 

Let’s go Red Sox!

 

Tom Duross