On Tue, Jul 27, 2021 at 7:28 AM Tom Duross via Sprinklerforum <
[email protected]> wrote:

> Good morning Campers.  Looking for advice and comments.
>
> I have an existing diesel driven fire pump in a prefabricated pump house
> installed in 2012 serving 2 apartment buildings.
>
> I first tested this pump in 2017, had 13 hours on it, ran fine but we ran
> out of water at just about 100% capacity.
>
> Spent the day with the water department a few days later checking
> underground valves, flowing a few street main’s hydrants, basically came to
> the conclusion that this is all we got.  Wrote up a report, suggested they
> hire an FPE to see if the pump’s tested capacity meets requirements, how
> did
> this happen, what about the hydrants off this system, stuff like that.  I
> think I stirred the sleepy caldron a little.
>
> Didn’t hear back from the client until this spring.  Apparently they
> changed
> ITM contractors and the new one didn’t pan out.  They had a balcony fire
> May
> 2021, gas grille, 13R system with no attic protection, non-completed attic
> separations and fire walls, etc.  Fortunately they had a response so
> quickly
> it never made it to penetrate the eaves and soffits and was extinguished
> between the 5th and 6th (top) floors.  Local FD must have had a field day
> with a Q20 of about 800 and closest city hydrant ¼ mile away.  Waiting for
> incident report to review.
>
>
>
> So back to my query.  It’s a xy&em pump house.  All welded sch40 and
> painted.  Not the greatest build as there’s a 6” BFP vertically installed
> right off the incoming service with elbows turning it around and down to
> the
> floor to feed the pump.  Just a few spacers in the piping so no room for
> slipping in this device unless something gets removed or moved.  4-15 of
> #20
> (2013) says between the pump discharge and check and I get that but also
> defers to the mfgr. for direction.  Looking at the various offerings most
> are a little vague on placement and even one says after the pump discharge
> valve.  Without major surgery, I have 2 spots to slip in this 20” long
> device.  I can remove the relief valve between the discharge increaser and
> pump check and put it there ‘or’ I can remove the tee feeding a 6” storz
> and
> check located between the discharge valve and the city bypass.  The former
> will allow me to test through the device but the latter will not.  I don’t
> believe either of these appurtenances are necessary and I will explain
> (he’s
> still rambling?  Jeepers….).  The engine is a small JD inline 4 running
> 3000
> rpm, single ECM, max. speed is 3300.  Churn is 155 at 3025.  I haven’t
> physically done it but if I extrapolate to 3300 I get 170 psi.  I’m below
> 175 so I think the PRV can go.  If I opt to remove the storz I can but
> testing this pump will have to be via the 3 hydrants it serves, in addition
> to the 2 buildings.  I honestly don’t know why the engineer (small E) had a
> storz included as this house it atop a hill in the woods ½ mile away from a
> city hydrant and these buildings.
>
>
>
> OK, done rambling.  Loose the PRV or keep scratching my head?
>
>
>
> Let’s go Red Sox!
>
>
>
> Tom Duross
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to