Did the specifying engineer state why he/she wants only Sch 40?
  
  
  
  
  
  
  

  
  
>   
> On Nov 22, 2022 at 12:14 PM,  <Skyler Bilbo 
> (mailto:sbi...@wenteplumbing.com)>  wrote:
>   
>   
>   
> I always use the Corrosion Resistance Ratio (CRR) argument.    Basically, the 
> thickness of schedule 10 piping is greater than or equal to the thickness of 
> the first exposed thread of threaded schedule   40.    Using this argument, 
> schedule 10 should theoretically last at least as long as threaded schedule 
> 40.    You can't use this argument   if they call for grooved schedule 40.  
>
>   
>
>   
> Thanks,
>   
>   
>   
>   
>   
>   
>   
>   
> Skyler Bilbo  
>
>     
> 1700 S. Raney Street
>   
> Effingham, IL 62401
>   
> 217-819-6404 Direct
>   
> 217-347-7315 Fax
>   
>
>   
> sbi...@wenteplumbing.com (mailto:sbi...@wenteplumbing.com)
>   
> www.wenteplumbing.com (http://www.wenteplumbing.com)
>   
>   
>   
>   
>   
>   
>   
>   
>   
>     
>   
>   
> On Tue, Nov 22, 2022 at 10:14 AM  <tston...@comcast.net 
> (mailto:tston...@comcast.net)>  wrote:
>   
> >   
> >   
> >   
> >   
> >
> > Are there any studies comparing the failure rates of Schedule 10 steel pipe 
> > versus schedule 40 steel pipe used on wet water filled sprinkler systems?
> >
> >   
> >
> > I have a client who is not allowing the use of schedule 10 Main piping 2 ½” 
> > and larger on their projects. All piping used has to be schedule 40.
> >
> >   
> >
> >   
> >
> >   
> >
> > Thank you in advance.
> >
> >   
> >
> >   
> >
> >   
> >
> > Regards,
> >
> >   
> >
> >  G. Tim Stone
> >
> >   
> >
> >     
> >
> >   
> >
> >  G. Tim Stone Consulting, LLC
> >
> >   
> >
> >  NICET Level III Engineering Technician
> >
> >   
> >
> >  Fire Protection Sprinkler Design
> >
> >   
> >
> >  and Consulting Services
> >
> >   
> >
> >     
> >
> >   
> >
> >       117 Old Stage Rd. - Essex Jct., VT. 05452
> >
> >   
> >
> >                                  CELL: (802) 373-0638     
> >
> >   
> >
> >                             tston...@comcast.net 
> > (mailto:tston...@comcast.net)
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >  _________________________________________________________
> >  SprinklerForum mailing list:
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> >  To unsubscribe send an email to  
> > sprinklerforum-le...@lists.firesprinkler.org 
> > (mailto:sprinklerforum-le...@lists.firesprinkler.org)      
> > _________________________________________________________ SprinklerForum 
> > mailing list: 
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > To unsubscribe send an email to 
> > sprinklerforum-le...@lists.firesprinkler.org            
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to