On backflow testing, NFPA 13 (2019) 16.14.5.1 states the backflow needs to be 
tested at system demand.
I have a hard cover copy, and in it the question was asked, if a 2" main drain 
would be sufficient, to do the backflow test.
After their explanation, they say it basically needs to be the same size as 
your system riser, and using a larger drain valve would be a waste since the 
drain test is to be done more often.
So what we've been doing is running a pipe outside the same size as the 
backflow, using a normally closed butterfly valve. Sometime routing around the 
FDC if it's a Storz. model.

Our thought now is why not run several 2" drains out the wall.
With 2½" & 3" backflows, we increase the main drain to 2" which is usually 
enough for system demand. Can always run a separate 1" insp. test also.
With 4" backflows, you already need (1) 2" main drain, why not run a separate 
one for testing, that will give you (2) 2" openings, and run a third if you 
have a 6" backflow.
And with multiple systems, run the main drains out separately instead of 
combining them together before you go out.

Does this sound feasible, since all we're really trying to do is exercise the 
springs in the checks?

From: Ed Kramer <[email protected]>
Sent: Friday, November 18, 2022 11:19 AM
To: [email protected]
Subject: [Sprinklerforum] BFP on underground supply

NFPA 13 is pretty clear that some method of forward flow testing a fire 
sprinkler system backflow preventer shall be provided.  If the BFP is located 
at the system riser (very common in these parts), we provide the required means.

So, who is responsible for providing the means if the BFP is located in a pit 
on the underground fire service, and the UG fire service (along with the 
pit/BFP) is "by others"?  From a practical viewpoint, it's easy enough for us 
to provide that at our system riser, but are we required to do so?  Or does 
that responsibility fall on whomever installs the BFP?  I've not seen this 
addressed anywhere in bid/contract documents.

Ed Kramer
Bamford Fire