NFPA 13 (2022) Section 16.4.5 with ‘enhanced content’ and some new standard 
language, discourages this practice.  How will the requirement of Section 
16.14.5.1.1 be achieved without additional calculation?:

16.14.5.1* Backflow Prevention Valves.

A test connection shall be provided downstream of all backflow prevention 
valves for the performance of forward flow tests required by this standard and 
NFPA 25 at a minimum flow rate of the system demand including hose allowance 
where applicable.

ENHANCED CONTENT

ASK THE SYSTEM DESIGNER

Is a main drain connection sufficient means for conducting the flow test at 
system demand required by 16.14.5.1?

This type of connection generally is not sufficient for conducting the flow 
test because main drains have not been sized to accommodate system flow. 
Backflow preventers have internally loaded springs that are constantly pushing 
the valves into the closed position. If the springs are not periodically 
exercised, they might not permit the valve to fully open when there is a fire, 
impairing the sprinkler system. To prevent that from happening, NFPA 25 
requires periodic forward flow tests of the backflow devices at the system 
demand flow. To ensure that the tests can happen, NFPA 13 requires the 
installation of a mechanism downstream of the backflow device that will allow 
the system demand to flow through the mechanism when it is opened.

Prior to the 2016 edition of NFPA 13, the largest main drain size was limited 
to 2 in. (50 mm), which allowed systems to be drained in a reasonable time 
period and conserved water during main drain tests. In the 2016 edition, the 
size of the main drain was permitted to be increased, but using large main 
drains to conduct forward flow tests of backflow preventers still might be a 
concern.

To create a flow at least as large as the system demand, an opening needs to be 
created with roughly the same cross-sectional area as the system riser. Doing 
so ensures that the system demand has been created when the mechanism is fully 
open without having to take any pressure or flow readings. On systems with a 2 
in. (50 mm) main drain, the cross-sectional area of the drain opening typically 
is insufficient to achieve the system demand flow.

When a main drain larger than 2 in. (50 mm) is used, the size of the system 
riser creates two potential problems. The first is that main drains generally 
are on the inside of a building, and providing sufficient drainage to deal with 
the discharge from the fully opened drain is a challenge. With 2 in. (50 mm) 
drains, sprinkler contractors frequently do not deal with the drainage 
situation correctly, and the drain cannot be opened fully. Using a larger drain 
might only exacerbate the issue.

The second problem is the main drain test itself, which requires the drain to 
be fully opened four times annually. With a large drain, water is wasted when 
the drain is fully opened. It might be tempting to not open the drain fully for 
the test, which makes comparison of the test results impossible to correlate.

A better solution would be a means to test the full flow of the backflow device 
that is separate from the main drain that allows for proper drainage. 
Paragraphs 16.14.5.1.1 through 16.14.5.1.3 are new for the 2022 edition and 
provide installation options to facilitate forward flow testing for systems 
equipped with backflow preventers.

16.14.5.1.1
A 2 1⁄2 in. (65 mm) hose valve shall be provided downstream of the backflow 
prevention valve for every 250 gpm (950 L/min) of flow rate required by the 
system demand including hose allowance where applicable.

16.14.5.1.2*
Existing hose connections downstream of the backflow prevention valve shall be 
allowed to be utilized.

16.14.5.1.3*
Other means shall be permitted as long as the system doesn't require 
modification to perform the test and it is sized to meet the system demand.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

[cid:[email protected]]

From: Dennis Wilson <[email protected]>
Sent: Wednesday, December 14, 2022 11:01 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: BFP on underground supply

On backflow testing, NFPA 13 (2019) 16.14.5.1 states the backflow needs to be 
tested at system demand.
I have a hard cover copy, and in it the question was asked, if a 2” main drain 
would be sufficient, to do the backflow test.
After their explanation, they say it basically needs to be the same size as 
your system riser, and using a larger drain valve would be a waste since the 
drain test is to be done more often.
So what we’ve been doing is running a pipe outside the same size as the 
backflow, using a normally closed butterfly valve. Sometime routing around the 
FDC if it’s a Storz. model.

Our thought now is why not run several 2” drains out the wall.
With 2½” & 3” backflows, we increase the main drain to 2” which is usually 
enough for system demand. Can always run a separate 1” insp. test also.
With 4” backflows, you already need (1) 2” main drain, why not run a separate 
one for testing, that will give you (2) 2“ openings, and run a third if you 
have a 6” backflow.
And with multiple systems, run the main drains out separately instead of 
combining them together before you go out.

Does this sound feasible, since all we’re really trying to do is exercise the 
springs in the checks?


From: Ed Kramer <[email protected]<mailto:[email protected]>>
Sent: Friday, November 18, 2022 11:19 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] BFP on underground supply

NFPA 13 is pretty clear that some method of forward flow testing a fire 
sprinkler system backflow preventer shall be provided.  If the BFP is located 
at the system riser (very common in these parts), we provide the required means.

So, who is responsible for providing the means if the BFP is located in a pit 
on the underground fire service, and the UG fire service (along with the 
pit/BFP) is “by others”?  From a practical viewpoint, it’s easy enough for us 
to provide that at our system riser, but are we required to do so?  Or does 
that responsibility fall on whomever installs the BFP?  I’ve not seen this 
addressed anywhere in bid/contract documents.

Ed Kramer
Bamford Fire



_________________________________________________________