Richad,

10.4.14 Use nitrogen or dry gas.
10.4.14.1 The pipe shall be pressurized to 40 psi (276 kPa).


Thomas Wellen, P.E.
Senior Fire Protection Consultant
Fire Engineering & Consulting, LLC
M: 972.355.2159
fireeac.com



> On Mar 27, 2023, at 5:17 AM, RACHID SAADAOUI <[email protected]> wrote:
> 
> 
> Hello,
> 
> I am in the start-up phase of a project to protect electrical rooms using a 
> NOVEC 1230 gas extinguishing system.
> 
> And I want to know, is the hydrostatic test of the piping installed required 
> by NFPA2001, if so, please communicate the NFPA article in detail
> 
> Thanks,
> RACHID SAADAOUI
> Head of technical department 
> OLP MORROCO
> 00212665648687 
> 