We use those remote fuel fill station fairly often because there are a few 
jurisdictions nearby that require it. Pryco is one company that makes them. But 
they are pretty expensive, so I’m not necessarily suggesting that it’s a good 
alternative.

-Kyle M

From: Jason Moore <[email protected]>
Sent: Wednesday, March 29, 2023 10:27 AM
To: [email protected]
Subject: [EXTERNAL] [Sprinklerforum] Economical Solution For Remote Diesel Fuel 
Fill

When installing a diesel fire pump fuel tank, the top of the tank in the pump 
room is generally higher than 5’ AFF.  The exterior fuel fill is required to be 
no more than 5’ above grade and usually ends up being about 7’ above grade.

In the past, we’ve used a permanently installed stair platform or a Morrison 
overfill prevention valve, shut-off valve, quick connect and spill containment 
box... neither option is economical.

We have several installs coming up and was looking for something better.  
Typically, the fuel delivery driver does not use the exterior fill and fills 
directly to the tank inside the pump room, but the exterior fill is still 
required to be within guidelines.

Any ideas?

Jason Moore
NICET IV #116350
Vegas Valley Fire
702-544-6508