Rachid,

NFPA 2001-22 states that before putting the system in service, pipes shall
be inspected to verify tightness of fittings, adequate pipe support,
bracing, and that nozzles have been installed according to their
orientation.

After that, piping shall be pressure-tested in a close circuit using
nitrogen or other dry gas (10.4.14).

The pipe shall be pressurized to at least 40 psi (10.4.14.1).

After removing the source of pressurizing gas, the pressure in the pipe
shall not be less than 80 percent of the test pressure after 10 minutes.
(10.4.14.2)

The pressure test shall be permitted to be omitted if the total piping
contains no more than one change in direction fitting between the storage
container and the discharge nozzle and if all piping has been physically
checked for tightness. (10.4.14.3)

A flow test using nitrogen or an inert gas shall be performed on the piping
network to verify that flow is continuous. (10.4.15).

Hoping this could be of help to you.

Best!



On Mon, Mar 27, 2023 at 5:17 AM RACHID SAADAOUI <[email protected]>
wrote:

> Hello,
>
> I am in the start-up phase of a project to protect electrical rooms using
> a NOVEC 1230 gas extinguishing system.
>
> And I want to know, is the hydrostatic test of the piping installed
> required by NFPA2001, if so, please communicate the NFPA article in detail
>
> Thanks,
> RACHID SAADAOUI
> Head of technical department
> OLP MORROCO
> 00212665648687
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]



-- 
=?Este mensaje se dirige exclusivamente a su destinatario y puede contener
información privilegiada o confidencial. Si no es Ud. el destinatario
indicado, queda notificado de que la utilización, divulgación y/o copia sin
autorización está prohibida en virtud de la legislación vigente. Si ha
recibido este mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su destrucción.


This message is intended exclusively for its addressee and may contain
information that is confidential and protected by professional privilege.
If you are not the intended recipient you are hereby notified that any
dissemination, copy or disclosure of this communication is strictly
prohibited by law. If this message has been received in error, please
notify us immediately via e-mail and delete it.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to