I don’t have the reference off hand, but if you go to the standard that covers 
spray booths and such, it says to just calculate all in the booth if less than, 
also including the duct exhaust.  So, I believe in that instance, you are OK to 
just calculate the paint booth only.  However, it is Friday at the end of a 
long week so I could be totally crazy in this thinking.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad

From: Anthony Johnson <[email protected]>
Sent: Friday, March 31, 2023 11:30 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Paint Booths Calculation

Hello everybody,

For a cabinet shop paint booth the overhead system was designed to an Ord Group 
II occupancy and the owner is now installing a spray booth. The last booth I 
sprinklered was over a decade ago and things have changed since then. In the 
past I would just calculate all the sprinklers in the booth. Now we have 
criteria for mixed occupancies which require a phantom flow at the most remote 
branchline if your system flow is less than density x sq. ft. (NFPA 27.2.4.2.4 
- 2019 ed). In the 2013 edition handbook there was an AHJ FAQ that brought up 
the exact scenario I'm in and said that you would comply with 27.2.4.2.4 
HOWEVER I noticed that the AHJ FAQ does not exist in the 2019 edition and at 
the end of the day it's just an AHJ FAQ and is not even appendix material so I 
know it carries no weight but I want to make sure I nail this right. On one 
hand I'm thinking this is not an area/density calc so I should just stick to 
calculating only the booth, maybe by appealing to the room design method OR 
take worse case scenario and add the considerable phantom gpm flow and 500 gpm 
hose allowance which would require major upgrades. Guidance and thought would 
be appreciated.

Thanks,

Anthony Johnson
Mountain Fire Protection
'Saving Lives and Valuing Property'

[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>
Virus-free.www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to