This allows you to do .4 times the booth and not .4 times 3000

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Anthony Johnson <[email protected]>
Sent: Friday, March 31, 2023 12:41 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Paint Booths Calculation

As an additional note NFPA 2019: 26.4.1.3<http://26.4.1.3> says that the 
sprinkler design area shall not be required to exceed the area of the booth so 
my question basically becomes is it still neccessary to add a phantom flow for 
the difference of flow?

Anthony